Group, The following is essentially the response that I made to Tom VandeWater at Dow Corning based on his request below. He asked that I post it to the group to the benefit of everyone. I hope it helps. Regards, Matt = ---------------- Tom, I have been monitoring the conversations in Cassandra, so I want to address one of the other topics first. = The FBM limit on the FCP270 should be taken as the 64 FBMs as specified in the PSS. I echo strongly the statements that Russ and Alex have made that the limit is 64. I know for a fact that if an FCP is loaded with 128 of a typical mix of non-digital protocol FBMs, and the normal block to IO ratio of 3 to 4, that there will not be sufficient performance in the FCP to handle it. (confirming your speculations) The 128 connection limit was put in place to eliminate hardware as a reason to limit the FCP capacity, and if a customer wanted to connect IO at slower speeds (say 2-5 seconds) for data acquisition purposes then they would have that ability. But also, if a customer has 64 FBMs on an FCP currently and they see that there is spare IO and block load capacity on the FCP, they will be able to add a 65 or 66 FBM without needing to add a controller or ask for special dispensation from Foxboro to do so. Now to your questions: The 128 limit for 200 series FBMs on a ZCP270 is a specification listed in the PSS and this is the limit that has been tested and will be supported via TAC. Exceeding these limits may make it difficult for any problems to be diagnosed and supported via the TAC Center, so we strongly do not recommend exceeding them. However... if you do exceed those ZCP limits, the system will likely work especially for just a couple modules, but it is untested functionality so unforeseen limits may be hit that are unrelated to performance and the number of FBMs specifically. (block size and execution limits, IPC, OM scanner tables, and other more esoteric aspects for instance) Performance, of course, will be a major stumbling block related not only to the traffic on the IO fieldbus, but also in block performance to support the number of blocks required for that IO quantity. So if you hit the 128 FBM limit, and you are contemplating exceeding it, I would be extremely cautious in doing so. And you do it at your own risk. Next question... As far as qualifying the system to exceed the limit, it is difficult to speculate how much work it would be and of course it depends on how many additional FBMs would be required (150 from your note below). We have found very few customers who are interested in exceeding that quantity of IO on a single controller. Most customers seem to prefer to segment their plant into distinct controllers so as to minimize the plant impact in case of operational issues with a particular controller. I do understand though your desire to minimize peer-to-peer comms due to your use of sequence blocks and one-shot sets and gets and the load that feature that puts on the system/network. But back to the question, as I said it is difficult to speculate what exceeding these limits would do, because the load increase on the IO bus is only the beginning of the potential issue. Other bottlenecks in the system would likely be hit that would require investigation as to how and if they could be exceeded. A program would start specifying the number of IO that is desired, loading up a system to that number of IO and other reasonable supporting configurations (displays, blocks, peer-to-peer, historians, etc.) and then run it through a full regression test of the system, and evaluate key systems to see what sort of tolerance margins are seen. And if problems ensue, which are likely, then it would take development resources to investigate, do risk assessments and project estimates to enhance the product to overcome the limit. Depending on what they find, it could be significant effort or nearly impossible to do. This sort of activity would be difficult to sponsor as it would consume much of the testing organization's hardware resources for a period of time (stalling current programs) or would require specifying, purchasing, and building a new lab for this purpose. Further, in my opinion, it is unlikely that we would invest development budget to pursue such an activity. Question 3: In a broad sense, your speculations resemble those by many of us internally in terms of where we think Foxboro should go in the future. There are many factors to consider though, and what make sense today changes over time. That's about as much as I can say. This answer is highly speculative and deliberately vague. I'm sorry but these sorts of discussions are dangerous in setting incorrect customer expectations, and I have been burned in the past by engaging in them too freely. = Regards, Matt DeAthos IA Series Product Management -----Original Message----- From: tom.vandewater@xxxxxxxxxxxxxx [mailto:tom.vandewater@xxxxxxxxxxxxxx] Sent: Tuesday, August 14, 2007 12:32 PM To: Deathos, Matthew Cc: Thomas, Bill Subject: RE: [foxboro] FCP's vs. ZCP selection on new projects Matt, Tom VandeWater here. You may have been following this thread on the Cassandra mail list. If not here are my questions? Is the 128 FBM limitation a gospel rule or could a user add more than that to a ZCP today? If it is a hard and fast rule, how difficult would it be to modify from Foxboro's perspective to allow a larger number of FBM's? Is there a CP with ZCP capabilities built in the form factor of an FCP being visualized in the future? Read on below for a better understanding of why I'm interested in this. Thanks for any feedback or insight you may have. -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of tom.vandewater@xxxxxxxxxxxxxx Sent: Tuesday, August 14, 2007 12:44 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FCP's vs. ZCP selection on new projects Alex, I understand the reasons for your response and have contacted Matt off list with my questions and requests. From my observation, several people on the list would like to see ZCP functionality in the FCP form factor. That has spurred Foxboro to try to expand the number of FBM's an FCP can host. I'm skeptical of whether an FCP would be very useable when hosting 128 FBM's, even across a 2MB/s RS485 bus. I am leery of sinking a lot of eggs in the FCP basket. I had a similar feeling about the Micro IA offering that was supposed to be a low cost control alternative, much like the FCP. We avoided them like the plague and now I am forever thankful. Tom -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Johnson, Alex P (IPS) Sent: Tuesday, August 14, 2007 11:42 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FCP's vs. ZCP selection on new projects The 128 FBM limit is the published specification. =3D3D I'm not going to make any comments on whether or not one can violation our specification without consequences because I'm not that crazy. :) As far as changing the limit is concerned, you'd have to take that up with Marketing - Matt DeAthos and Betty-Naylor. I hope this helps and I do understand the issue. Regards, Alex Johnson Invensys Systems, Inc. 10900 Equity Drive Houston, TX 77041 713.329.8472 (voice) 713.329.1700 (fax) 713.329.1600 (switchboard) alex.johnson@xxxxxxxxxxxxxxxx -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of tom.vandewater@xxxxxxxxxxxxxx Sent: Tuesday, August 14, 2007 11:17 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FCP's vs. ZCP selection on new projects Below is an actual case study based on our experience with CP-60's. We initially used multiple FBI10E's, (10MB E-Net to 268KBS RS-485), to communicate with our 100 series I/O. We limited each FBI10E to host no more than 24 FBM's. We were able to communicate with 120 FBM's and the Fieldbus scan as a percentage of Total Control Cycle was only 32 percent, or about .25 percent loading per attached FBM. Being good customers, we complained about the cost of all the FBI10E's and the clumsiness of the thin net to connect them to the CP-60 fieldbus. Foxboro responded and said we could save a lot of money and thin net if we used one set of DCM10E's, (10MB E-Net to 268KBS RS-485), and connected all of our pre-existing old style FBI segments to it using the same Belden twin-ax that was in place from previous CP10's, 30's, and 40's. We said that sounds great and we installed it that way. We were able to communicate with 59 FBM's and the Fieldbus scan as a percentage of Total Control Cycle was 55 percent, or about 1.00 percent loading per attached FBM. In addition, we had huge numbers of fieldbus communication errors on the CP using the DCM in this arrangement. Alex said in his note on this subject: "a lot of the I/O performance of the ZCP comes from a strong co-processor in the box plus the parallelism of the FCMs." I am sure he is correct. As such there should be no expectation that a FCP using today's design will ever be a suitable replacement to communicate with as much I/O as a ZCP. I expect that trying to communicate with 120 FBM's via a single 2MB/s RS485 fieldbus used by the FCP will be about "ONE FOURTH" as efficient as using distributed FCM100 segments communicating at 100MB/s to a ZCP so everyone should be aware of that very real limitation. Corey Clingo summed it up best for me when he said: "Like Tom, I like the ZCP's capabilities and the FCP's form factor." Here are more specific reasons for my request: =3D3D3D20 Using the 200 series baseplates and I/O form factor, (less depth), we have been able to achieve double sided, (back-to-back), mounting in the same 19" rack. That allows us to share power distribution and fiber communication infrastructure over 8 baseplates instead of 4 1x8's like we used in the past for 100 series I/O. With an FCP form factor we could mount the CP's in the same rack space. The depth of the 1x8's used for the ZCP's takes up the entire space, (front-to-back), in a standard 19" rack. In addition, our processes are large enough to require 80 to 150 FBM's. This is too much for an FCP, but we now see that a ZCP could easily handle that kind of load. One of our ZCP's communicates with 82 200 series FBM's and uses 20 percent for field bus scan. Again, about 0.25 percent loading per attached FBM. There is an advantage for us to be able to fit each process in its own CP. Peer-to-peer becomes more undesirable as we increase our sequence automation. Change deltas and timing for values being passed between CP's is an issue with peer-to-peer but if all control for a process is in one CP there is no need to use object manager resources to get and set the values and a more timely and robust execution is achieved. That is my reason for wanting Foxboro to allow a larger number of FBM's connected to a ZCP that can clearly handle the additional load. Questions to Alex or Russ: Is the 128 FBM limitation a gospel rule or could a user add more than that to a ZCP today? If it is a hard and fast rule, how difficult would it be to modify from Foxboro's perspective to allow a larger number of FBM's? Thanks again for any feedback, Tom VandeWater Control Systems Developer/Analyst Dow Corning Corporation Carrollton, KY USA -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Boulay, Russ Sent: Tuesday, August 14, 2007 8:05 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FCP's vs. ZCP selection on new projects The FCP270 uses FEM100's to go beyond 32 FBM's With the FEM100 only one pair is allowed. 4 ports going to 4 basplates each. So, FEM100 is trying to do all the work. So, number per sizing spreadsheet will vary from 64 to 128 FBM's depending on what your asking the FCP to do. The ZCP270 can use multiple pairs of FCM100's to split it's fieldbus load. 32 FBM's per FCM100 Multiple FCM100's drops the I/O load on a ZCP Thus allowing more FBM's -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Kinsinger, Matthew R Sent: Tuesday, August 14, 2007 7:58 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FCP's vs. ZCP selection on new projects I took a class at Foxboro last week. We were interested in the new V8 =3D3D3D3D3D stuff and learning about IACC so I only took 2001V8. Alan Leslie, the =3D3D3D3D3D person teaching the course, made it very clear the FCP270 now supports =3D3D3D3D3D 128x 200 series FBMs and 64 100 series. I notice many of you are still =3D3D3D3D3D focusing on the original 32 then 64 200 series supported. =3D3D3D3D3D20 With the 128 supported, is the FCP still using FEM's instead of FCM's? =3D3D3D3D3D Is that the limiting difference? Matt Kinsinger Process Control Engineer=3D3D3D3D3D20 PPG Barberton 330-825-1208 -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] =3D3D3D3D3D On Behalf Of Corey R Clingo Sent: Tuesday, August 14, 2007 1:51 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FCP's vs. ZCP selection on new projects I've been watching this whole FCP vs. ZCP discussion with some interest. =3D3D3D3D3D It seems to me on the surface that control system vendors today are =3D =3D3D3D =3D3D3D3D3D going=3D3D3D3D3D20 to a model of more controllers with fewer I/O cards per controller, I=3D3D3D3D3D20 presume to "reserve" more power in the controller for advanced =3D3D3D3D3D algorithms=3D3D3D3D3D20 as well as simplify the system architecture (particularly if they don't=3D3D3D3D3D20 allow I/O remote from the controller at all). Of course as you split =3D3D3D3D3D your=3D3D3D3D3D20 plant amongst more controllers, the amount of peer-to-peer you end up=3D3D3D3D3D20 doing probably increases. I wonder how the industry in general is =3D3D3D3D3D dealing=3D3D3D3D3D20 with that (besides going to faster networks, of course). I don't have any CPs right now that have more than 61 FBMs, but if the =3D3D3D3D3D FCP=3D3D3D3D3D20 is limited to 64, I would likely split a 50+ FBM CP40 up into two FCPs =3D3D3D3D3D if=3D3D3D3D3D20 I were going to use those, just so I could have a few more spare I/O. =3D3D3D3D3D I'd=3D3D3D3D3D20 probably end up doing some more P2P though to effect that split. P2P =3D3D3D3D3D has=3D3D3D3D3D20 worked well for me in the past, but I use it sparingly. Is it any =3D3D3D3D3D better=3D3D3D3D3D20 on the FCP than, say, a CP60? Like Tom, I like the ZCP's capabilities and the FCP's form factor. Corey Clingo BASF Corporation "Johnson, Alex P \(IPS\)" <alex.johnson@xxxxxxxxxxxxxxxx>=3D3D3D3D3D20 Sent by: foxboro-bounce@xxxxxxxxxxxxx 08/13/2007 11:11 PM Please respond to foxboro@xxxxxxxxxxxxx To <foxboro@xxxxxxxxxxxxx> cc Subject Re: [foxboro] FCP's vs. ZCP selection on new projects I'll give it a try. Re: I guess the FCP's were initially developed as a lower cost alternative. True. They were also expected to serve as a way to enter new markets once they are self-hosting. Re: It is my understanding that the the FCP's have the same horsepower with the exception that they don't have fast =3D3D3D3D3D3D Ethernet fieldbus communication. =3D3D3D3D3D3D True enough, but a lot of the I/O performance of the ZCP comes from a strong co-processor in the box plus the parallelism of the FCMs. Re: Adding that capability would make the FCP's a lot more flexible and would make it easier for them to communicate with multiple distributed segments of I/O in the same way as the ZCP's The original plan was to offer three CP270s: 1) Field mounted (FCP) for use in situations where the controller would be Field mounted. 2) Z-module (ZCP) form factor to allow the reuse of the cabinets and =3D3D3D3D3D3D power supplies owned by our installed base. 3) Rack mounted (RCP) which was to be - basically - ZCP in a DIN rail mounted tin can. We built the first two. I suppose one could argue about the product mix, but we felt the ZCP was important to the installed base. Clearly as we look forward to new CP hardware, the mix may change. Re: PSSs The specification sheets are correct. Re: Does Foxboro have plans to release a CP in the FCP form factor that uses a Fast Ethernet Fieldbus? Not in the near term. Re: Has Foxboro considered increasing the number of FBM's that a ZCP can communicate with? It has been stressed test well beyond 128, but we don't see a compelling reason to increase the published limit on the ZCP. =3D3D3D3D3D3D Most new jobs find the FCP to offer a better $ per I/O point ratio. Moreover, even in the installed base, a large number locations are interested in using the FCP to free space in their rack room. An FCM takes the same space as an FCP so unless there is a truly compelling reason, most folks don't use the ZCP. They remove the old racks and use the FCP. Given the above, we've worked to improve the $ per I/O point ratio of the FCP as being the best short-term approach for our clients. Regards, Alex Johnson Invensys Systems, Inc. 10900 Equity Drive Houston, TX 77041 713.329.8472 (voice) 713.329.1700 (fax) 713.329.1600 (switchboard) alex.johnson@xxxxxxxxxxxxxxxx =3D3D3D3D3D20 =3D3D3D3D3D20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D3D3D3D3D20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: =3D3D3D3D3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3D3D3Djoin to unsubscribe: =3D3D3D3D3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3D3D3Dleave =3D3D3D3D3D20 =3D3D3D3D =3D3D3D3D _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D3D3D3D foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3D3Djoin to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3D3Dleave =3D3D3D3D Confidentiality Notice: The information contained in this electronic message and any attachment(s) =3D3D3D3D to this message are intended for the exclusive use of the recipient(s) and =3D3D3D3D may contain confidential, privileged or proprietary information. If you are=3D3D3D3D not the intended recipient, please notify the sender immediately, delete a=3D3D3D3D ll copies of this message and any attachment(s). Any other use of the E-Mai=3D3D3D3D l by you is prohibited. =3D3D3D20 =3D3D3D20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D3D3D20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: =3D3D3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3Djoin to unsubscribe: =3D3D3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3Dleave =3D3D3D20 =3D3D =3D3D _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D3D foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3Djoin to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3Dleave =3D3D Confidentiality Notice: The information contained in this electronic message and any attachment(s) =3D3D to this message are intended for the exclusive use of the recipient(s) and =3D3D may contain confidential, privileged or proprietary information. If you are=3D3D not the intended recipient, please notify the sender immediately, delete a=3D3D ll copies of this message and any attachment(s). Any other use of the E-Mai=3D3D l by you is prohibited. =3D20 =3D20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin to unsubscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave =3D20 = = _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html = foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave = Confidentiality Notice: The information contained in this electronic message and any attachment(s) = to this message are intended for the exclusive use of the recipient(s) and = may contain confidential, privileged or proprietary information. If you are= not the intended recipient, please notify the sender immediately, delete a= ll copies of this message and any attachment(s). Any other use of the E-Mai= l by you is prohibited. _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave