It appears that your errors are 100 Series FBM related since FCM10E are
fine while DCM10E and FBI10E are not.
Check your terminations. With your setup there may be several
terminations in a fieldbus both resistor and bnc. Check carefully.

As to the counters;
The GCS website knowledgebase has two FAQ's when you query on PIOEFT.
________________________________________________________________________
FAQ180
FAQ
What are PIOEFT and PIOEGB counters? What do they convey, and how can
they be monitored?
March 28, 2008
  
Question
What are PIOEFT and PIOEGB counters? What do they convey, and how can
they be monitored?

Answer
A PIOEFT counter (or FT Mismatch) keeps track of the number of PIO input
mismatches on the Fieldbus. 
  
This occurs if the Primary and the Shadow CPs receive different data
from the FBMs. A non-zero number indicates possible hardware problems:
with one of the two CP modules or the X bus connection, or bad FBM
module, or bad FCM module, or cable, or terminator. PIOEGB (or FBM State
Change) keeps track of the number of good to bad FBM status transitions.


It is common for this counter to be non zero during system startup and
checkout, but it should not increment during stable system operation.
This counter can increment prior to FBM going offline/online messages in
System Monitor. If this counter increases over time, the System should
be monitored for FBM or Fieldbus problems. 

Possible fieldbus problems are: noise, old EEPROM revision, old hardware
revision, bad cables, bad connectors, bad terminators or bad terminating
resistors. 

For more information on both counters, refer to document B0193AX (vol 3)
Integrated Control Block and Aim for the section about Station Block
Parameters. 
__________________________________________________
Solution 235
How do I reset error counters in the CP Station Block from the command
line?
February 21, 2008
 
Problem Description

There are several counters in the Control Processor Station Blocks that
can be reset from the Station Block Default Display. How do I use the
command line to reset counters?

The parameters are retrieved using:

omget LTRBUG_STA:STATION.OMOVRN

omget LTRBUG_STA:STATION.CUMOVR

omget LTRBUG_STA:STATION.PIOEGB, also PIOEFT and PIOE1R


Fix/Resolution
These counters are reset to zero by by setting the respective reset
boolean parameter to True:

Use these commands:

omset -b T LTRBUG_STA:STATION.RSOMOV

omset -b T LTRBUG_STA:STATION.RESOVR

omset -b T LTRBUG_STA:STATION.PIORST


 
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Ajit.S.Kumar@xxxxxxxxxxxxx
Sent: Wednesday, November 12, 2008 07:12 AM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] PIO Bus access error on "A" or "B"

Dear Experts,
We are facing few problems with our CP 30 ,40,60s ...It keeps failing
with 
PIO Bus access error on "A" or "B". After reboot it works fine for
couple 
of days / months and fails again.
Replacement of CP is still the same. No Improvement. Grounding has been 
checked and ferrite installed for CP60. Noticed there is no problem of 
repeated failure of CP60 with FCM10E, but DCM10E and FBI10E the failure 
are seen escalating.
Secondly , Could anybody let me know why the Compound / Block and OB 
Overruns are very high, and I would like to know what's 
PIOE1R,PIOEFT,PIOEGB ..Is there a good manual where I could get the 
information and Can these counters be reset.
Thanks in advance 
Regards
Ajit kumar
Saudi aramco Mob. Refinery.

IDLETM = Idle Time;  CUMOVR = Cmpnd/Blk Overruns; OMOVRN = OM Overruns
PIOE1R = FB Retries; PIOEFT = Fault Tolerant Output mismatches
PIOEGB = Good->Bad FBM state changes; PP_NFD = Points NOT Found

CPLBUG  IDLETM  CPLOAD    CUMOVR  OMOVRN   PIOE1R  PIOEFT PIOEGB PP_NFD

A1CP01   47.3   19.60     52655  463152       0      48     609   0
A1CP02   79.4    7.00         0       0       0       0       0   0
A1CP03   84.8    6.80         0     305       0       0       0   0
A1CP04   68.2   11.80        66      16       0       0       0   0
A1CP05   84.3    4.60   1666732   8333        0       0       0   0
A2CP01   40.6   21.00      6262   20247       0      51     114   0
A2CP02   70.4   13.60         1   65580       0       0       0   0
A2CP03   69.3   13.60         0   28613       0       0       0   2
A2CP04   90.0    5.40         0       0       0       0       0   0
A2CP05   88.5    2.60         0      86       0       0       0   0
B1CP01   68.4   19.00     24988  112043       0     268    3253   0
B1CP02   76.8    6.00         0      26       0       0       0   0
B1CP03   70.1   11.20         1      11       0       0       0   0
B1CP04   73.4   21.80   5421794  87795        0       0       0  11
B1CP05   77.5    9.40   1666891 381400        0       0       0   0
B2CP01   81.7   12.40      3878    3294       0      53     236   1
S1CP01   79.4   18.20         2     502       0       5       0   0
S2CP01   64.4   32.00         4     382       0       7      69   0
S7CP01   70.2   25.80         8     623       0       8      19   0
S1CP03   82.9   86.00       650     388       0     698   22145   0
S1CP04   88.6   31.20       866     579       0       2   12274   0
S2CP04   91.8   25.00         0     945       0       0    2185   0
S3CP03   90.6   23.80        17     566       0      93    3299   0
S3CP04   92.4   24.00         2     319       0      24    4940   0
S3CP05   89.1   22.00        70      91       0    3726    5910   1
S4CP01   90.8   38.20      1575    2236       0       3    5296   0
S4CP03   93.0   16.40         4    2158       0      10    1802   0
S5CP02   85.4   50.00       668     302       0       4    2803   0
S5CP04   92.4   10.20         0     237       0       1      84   0
S5CP05   82.3   44.00       439     398       0      29    7315   0
S7CP03   90.0   20.80         0     411       0       0    1082   0
S8CP01   90.4   36.00       835      90       0       1    4262   0
S8CP02   84.0   78.60       776     207       0    1959   59147   0
S8CP03   86.2   62.00        92     145       0     305    7839   4
S8CP04   94.3   22.40         0      61       0       2     240   0
S8CP05   88.4   26.80         3     216       0       7    1100   0
S9CP02   86.1   66.00      2137     331       0  215664   25935   0
S9CP03   90.2   22.40         0     765       0       0     155   0
OMCP12   53.5   50.40         0       0       0       0      18   0
OMCP17   87.6    4.00         0       0       0       0     672   0
S1CP12   64.1   42.60         0     228       0       0     175   0
S2CP12   77.4   22.20         0     174       0       0       0   0
S2CP13   71.1   33.60         0     393       0       0      44   0
S3CP11   69.7   36.20         0     410       0       0      37   0
S3CP12   70.4   32.00         0     244       0       0      50   0
S3CP16   79.7   28.80         0      41       0       0    1346   0
S3CP17   80.6   28.00         0      48       0       0      78   0
S3CP18   80.2   28.00         0      31       0       0     127   0
S4CP12   75.9   28.40         0    1519       0       0       0   0
S5CP11   72.6   26.00         0     296       0       0      93   0
S5CP13   67.0   38.00         0     239       0       0       2   0
S6CP11   76.5   26.80         0     237       0       0    2061   0
S6CP12   71.1   32.00         0     142       0       0     104   0
S6CP13   81.1   19.00         0     221       0       0    4367   0
S6CP14   80.7   20.20         0     265       0       0      97   0
S6CP15   77.5   28.40         0     104       0       0    9335   0
S6CP16   82.9   20.00         0      35       0       0    4509   0
S6CP17   80.6   13.00         0     143       0       0     126   0
S6CP18   74.2   38.00         0       5       0       0       0   0
S7CP12   71.3   32.00         0     364       0       0       3   0
S9CP11   73.2   34.00         0     668       0       0      76   0



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 


* Confidentiality Notice:
This e-mail and any associated files are intended solely for the individual or 
entity to whom they are addressed. Please do not copy it or use it for any 
purposes, or disclose its contents to any other person. Further, this e-mail 
and any associated files may be confidential and further may be legally 
privileged. This email is from the Invensys Process Systems business unit of 
Invensys plc which is a company registered in England and Wales with its 
registered office at Portland House, Bressenden Place, London, SW1E 5BF 
(Registered number 166023).  For a list of European legal entities within the 
Invensys Process Systems business group, please click here 
http://www.invensys.com/legal/default.asp?top_nav_id=77&nav_id=80&prev_id=77.

If you have received this e-mail in error, you are on notice of its status. 
Please notify us immediately by reply e-mail and then delete this message from 
your system. Thank you for your co-operation. You may contact our Helpdesk on 
+44 (0)20 7821 3859 / 2105 or email inet.hqhelpdesk@xxxxxxxxxxxxx This e-mail 
and any attachments thereto may be subject to the terms of any agreements 
between Invensys (and/or its subsidiaries and affiliates) and the recipient 
(and/or its subsidiaries and affiliates).


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: