Summary: As indicated by Howard Cossitt, the bright green background indicates that the ERROR bit is set on the affected parameters. In this case, the root cause of the error was diagnostic messages coming from the transmitter via HART. Diagnosis: After reviewing the responses from yesterday, I checked the error status of the affected paramaters by connecting <compound>:<block>.<parameter>..E to a boolean input of a CALC block and confirmed that the ERROR bit was indeed turned on. (The syntax for connecting the ERROR status bit is shown on page 51 of B0700AG rev. D. Thanks again to Howard for the documentation reference. Note the two periods between parameter name and E.) Also, as suggested by Reed Cutshall, I used omget to check the DDIAG1 parameter of the upstream ECB; this returned a value of 85. Although the ECB is showing as good (white) in System Management, a closer look revealed the following status messages on page 3 of the Equip Info: Primary Out of Limits Primary Output Saturated More Status Available Configuration Changed A check of the documentation for the DDIAG1 parameter indicates that these messages correspond to bits 0, 2, 4, and 6, which do indeed add up to 85 (decimal). Thanks to all who responded. Greg Hurwitt BASF Freeport _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave