Alex and Tim,

It can be done in the Display Configurator using
SELECT
FUNCTION
execute program
and then typing in the following command:

dmcmd toggle CMPD:BLK.CINMSK.B1=20
where .B1 is equal to CINMSK for CIN_1 and .B32 is equal to CINMSK for
.CIN_32

Not sure how you do it in FoxView but I don't think that is an issue
with Tim.  Tim I will forward a DM compatible graphic as an attachment
that you can FTP to your UNIX system if you want one.  Let me know.

Tom VandeWater
Control Systems Developer/Analyst
Dow Corning Corporation
Carrollton, KY  USA

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Johnson, Alex P (IPS)
Sent: Friday, August 04, 2006 3:08 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Trying to set CINMSK in a MCIN block through a
display

Sadly, FV/DM do not allow you to toggle a single bit in a packed
Boolean.
=20

So, try this:

=20

1)    Create two MCOUT blocks and an MCIN block

2)    Put all three in simulation mode (IOMOPT=3D0)

3)    Put all three in automatic mode

a.    MA=3D1 and

b.    INITMA=3D1 and/or=20

4)    Connect the MCOUT PAKCRB output of the first MCOUT block to the
II01 parameter of the new MCIN block.

5)    Connect the MCOUT PAKCRB output of the second MCOUT block to the
II02 parameter of the new MCIN block.

6)    Connect the PAKCIN parameter of the new MCIN block to the CINMSK
parameter of the MCIN block with the "problem".

7)    Build your graphic to allow you to toggle any of the 16 MCOUT
input parameters (IN_1 to IN_16) in each of the two blocks.

=20

In this configuration, the display will change a bit in the input of one
of the MCOUTs. The MCOUTs will update their PAKCRB output. The PAKCRB
output will drive the new MCIN which will consolidate its inputs into a
single 32 bit packed long - PAKCIN. The PAKCIN parameter will mask the
inputs to the original/old MCIN.

=20

Make sense?

=20

Regards,

=20

Alex Johnson

Invensys Systems, Inc.

10900 Equity Drive

Houston, TX 77041

713.329.8472 (voice)

713.329.1700 (fax)

713.329.1600 (switchboard)

alex.johnson@xxxxxxxxxxxxxxxx

=20

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]

Sent: Friday, August 04, 2006 12:15 PM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Trying to set CINMSK in a MCIN block through a
display

=20

  I currently have a MCIN block that occasionally will read faulty data
at point 31.  I know that I can set the CINMSK to "2" instead of "0" to
disable the point.  Looking in a reference book I see that CINMSK is
settable and connectable but it is a "pack_l" input as opposed to real,
boolean, integer or string.

  Currently to change this point I need to go into the configuration,
make the change and it CHECKPOINTS as part of exiting.  I would like to
make a simple button on a screen (or a text input) that I can change the
CINMSK between 0 and 2 without causing the whole CP to checkpoint.
ideally the one action would also set CIN_31 to true.

  I am not familiar enough with the system to create a button that will
do this.  I have copied buttons before that toggle a point and changed
it to the point I need to toggle but that is as far as it goes.

  The system was initially installed around 1990 and uses the same
program to make displays as it did back then.  It is a UNIX system.

=20

Any help would be appreciated.

=20

Sincerely,

Timothy Healey

Facility Engineer

Wyeth

=20

=20

=20

_______________________________________________________________________

This mailing list is neither sponsored nor endorsed by Invensys Process

Systems (formerly The Foxboro Company). Use the info you obtain here at

your own risks. Read http://www.thecassandraproject.org/disclaimer.html

=20

foxboro mailing list:             //www.freelists.org/list/foxboro

to subscribe:         =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin

to unsubscribe:      =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave

=20


=20
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
=20
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe:      =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
=20
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: