Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley

  • From: "Landry, Scott" <Scott.Landry@xxxxxxxxxxxx>
  • To: "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>
  • Date: Sun, 2 Mar 2014 11:07:58 -0500

  Sandy,


    Some suggestions for you since this seems to be a new installation;


  #1  make sure you are using equivalent or higher revision of the 
        FBM224/FBM230/FBM231 Termination assembly below;

        P0926GH rev. E (compression screw)  
        P0926PA rev. B (Ring Lug) 


  #2   Close C5 and C6 on the RS232 DIP switches,  all others on A, B and C 
should be Open.

  #3   Use the latest Documents,  B0700AH-N  and  B0700BG-H

  #4   Use the latest driver,  V2.3.4

  #5   Use the latest FBM230 firmware,  V1.35

  #6   Use the latest FDSI configurator,  V1.4

  #7   With the latest driver, configure all the diagnostic counter blocks for 
ECB200 and ECB201 
         These will help you determine the best TO=  setting  plus give a 
wealth of information on how the interface is
         performing.  You could create a graphic with this information for easy 
access. 

  #8   Determine if the RedLion is capable of Heartbeat and then determine 
which of the 3 heartbeat methods to use.

  #9  Kevin brought up a good point about having more than one Master on the 
bus at the same time and to know what exception
         codes are being returned from the PLC >> RedLion >> FBM230.



    Regards,



    Scott

________________________________________
From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of 
Sandy AH [aloy_sah@xxxxxxxxx]
Sent: Sunday, March 02, 2014 3:29 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley

Dear Scott,
                       Please find details in Blue as given below.
Thanks and Regards,
Sandy
---------------------------------------------------------------------------------------------------------------------------------------
     Please provide more background info;

     T/A switch settings,  RS-232 settings matter even though you are using 
RS-485
               Port-1
                                A             B             C
                01           OPEN    OPEN    CLOSE
                02           CLOSE   CLOSE   OPEN
                03           OPEN    OPEN    OPEN
                04           CLOSE   CLOSE   OPEN
                05           CLOSE   OPEN    OPEN
                06           OPEN    OPEN    OPEN
                07           OPEN    OPEN    OPEN
                08           OPEN    CLOSE   OPEN
                Port-2/3/4
                ALL SWITCHES ARE IN CLOSE CONDITION
     T/A RS-485 termination setting ?
                Port-1/2/3/4
                TX – OPEN
RX - CLOSE
     FDSI driver type
                MODBUS.ZIPH
     FDSI driver revision
1.1 CRC F706988
     FDSI firmware level
SW: 1.31/0226
EEPROM: 0113/1.C7
     FDSI port configuration settings
Port : 1
Mode: RS485
Baud rate : 9600
Stop bit: 1
Databit: 8
Parity : None
Driver: MODBUS/RTU+TO

     FDSI xml configuration (if used)
                PORT CONFIGURATION:
Port : 1
Mode: RS485
Baud rate : 9600
Stop bit: 1
Data bit: 8
Parity : None
Driver: MODBUS/RTU+TO
                DEVICE CONFIGURATION:
DEFAULT SETTING

     FDSI ECB201 configuration
DEVNAME: 1
DEVOPTS: MODBUS+TO 0
FILEID: OPV001DEV.XML
     How many DCI blocks (how many of each type and period/phase)
RIN -43 & BIN – 24 (Phase -0 and Period – 2Sec)
     Allen-Bradley PLC Type
Allen-Bradley L62 Processor
     Allen-Bradley PLC interface card to FDSI type
Red lion (MODEL DSP - DATA STATION PLUS)
     Communications settings in  interface card to FDSI
Interface device communicating to AB PLC by using Ethernet communication and 
communicating to FBM230 by using RS485
      Is your RS-485 loop properly terminated and grounded ?
TXA and TXB properly terminated at both of ends. Grounding done at PLC Side
      Is your RS-485 loop properly installed and separated from EMI sources ?
                PLC cabinet is placed in the Field. This Cabinet is Purge 
protected and suitable for Zone-2 2A
      Did you configure any counter blocks for the ECB200 and ECB201(s) ?
Not Configured
----------------------------------------------------------------------------------------------------------------------------------------------------------------------



On Saturday, March 1, 2014 5:50 PM, "Landry, Scott" <Scott.Landry@xxxxxxxxxxxx> 
wrote:



     Sandy,


     Please provide more background info;

     T/A switch settings,  RS-232 settings matter even though you are using 
RS-485

     T/A RS-485 termination setting ?

     FDSI driver type

     FDSI driver revision

     FDSI firmware level

     FDSI port configuration settings

     FDSI xml configuration (if used)

     FDSI ECB201 configuration

     How many DCI blocks (how many of each type and period/phase)

     Allen-Bradley PLC Type

     Allen-Bradley PLC interface card to FDSI type

     Communications settings in  interface card to FDSI

      Is your RS-485 loop properly terminated and grounded ?

      Is your RS-485 loop properly installed and separated from EMI sources ?

      Did you configure any counter blocks for the ECB200 and ECB201(s) ?



      Regards,


       Scott



________________________________________
From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of 
aloy_sah@xxxxxxxxx [aloy_sah@xxxxxxxxx]
Sent: Saturday, March 01, 2014 1:12 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley

Brian,
I have tried to put 2 second,  30 second, timeout but the problem still 
persist. Once there is any break in the communication, then manually I have to 
disable then enable communication from SMDH.

Regards,
Sandy
Sent from my Phone

-----Original Message-----
From: Brian Long <blong@xxxxxxx>
Sender: foxboro-bounce@xxxxxxxxxxxxx
Date: Fri, 28 Feb 2014 21:49:36
To: foxboro@xxxxxxxxxxxxx<foxboro@xxxxxxxxxxxxx>
Reply-To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley

Probably need to add more time to timeout, see manual for details.
Sorry to not be more help, I'm not close to any docs.

Brian

Sent from my iPad

On Feb 28, 2014, at 9:24 PM, Sandy AH <aloy_sah@xxxxxxxxx> wrote:

> Hi there,
> I am interfacing FBM230 with PLC Allen Bradley over RS485.
> The modbus data is Holding Register Floating Point (4 bytes) with all modbus 
> configuration as per the configuration in PLC. Everything is showing healthy 
> on communication and I can get the data in RIN and BIN blocks.
> But after sometimes (let's say few hours) the communication fails (it shows 
> the device fail) and not automatically back to normal. I have to disable 
> communication and then enable communication in SMDH. Once I did this, the 
> communication immediately back to normal.�
> For example if I disconnect the cable (RS485 cable) and connect it back, the 
> communication to PLC AB does not back to normal automatically, it requires me 
> to disable/enable communication in SMDH first in order to make the 
> communication back healthy.
> Is there anyone can help on this since it is quite disturbing that I have to 
> disable / enable the communication every time there is a break in the 
> communication.
>
> Regards,
> Sandy - QAFAC
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list:            //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>


_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:            //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave



_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:            //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
*** Confidentiality Notice: This e-mail, including any associated or attached 
files, is intended solely for the individual or entity to which it is 
addressed. This e-mail is confidential and may well also be legally privileged. 
If you have received it in error, you are on notice of its status. Please 
notify the sender immediately by reply e-mail and then delete this message from 
your system. Please do not copy it or use it for any purposes, or disclose its 
contents to any other person. This email comes from a division of the Invensys 
Group, owned by Invensys Limited, which is a company registered in England and 
Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 
7AW (Registered number 166023). For a list of European legal entities within 
the Invensys Group, please select the Legal Entities link at invensys.com. 
Invensys Limited is owned by the Schneider-Electric Group.

You may contact Invensys Limited on +44 (0)20 3155 1200 or e-mail 
reception@xxxxxxxxxxxx. This e-mail and any attachments thereto may be subject 
to the terms of any agreements between Invensys (and/or its subsidiaries and 
affiliates) and the recipient (and/or its subsidiaries and affiliates).




_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:            //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
*** Confidentiality Notice: This e-mail, including any associated or attached 
files, is intended solely for the individual or entity to which it is 
addressed. This e-mail is confidential and may well also be legally privileged. 
If you have received it in error, you are on notice of its status. Please 
notify the sender immediately by reply e-mail and then delete this message from 
your system. Please do not copy it or use it for any purposes, or disclose its 
contents to any other person. This email comes from a division of the Invensys 
Group, owned by Invensys Limited, which is a company registered in England and 
Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 
7AW (Registered number 166023). For a list of European legal entities within 
the Invensys Group, please select the Legal Entities link at invensys.com. 
Invensys Limited is owned by the Schneider-Electric Group.
 
You may contact Invensys Limited on +44 (0)20 3155 1200 or e-mail 
reception@xxxxxxxxxxxx. This e-mail and any attachments thereto may be subject 
to the terms of any agreements between Invensys (and/or its subsidiaries and 
affiliates) and the recipient (and/or its subsidiaries and affiliates).

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 