Sandy, Some suggestions for you since this seems to be a new installation; #1 make sure you are using equivalent or higher revision of the FBM224/FBM230/FBM231 Termination assembly below; P0926GH rev. E (compression screw) P0926PA rev. B (Ring Lug) #2 Close C5 and C6 on the RS232 DIP switches, all others on A, B and C should be Open. #3 Use the latest Documents, B0700AH-N and B0700BG-H #4 Use the latest driver, V2.3.4 #5 Use the latest FBM230 firmware, V1.35 #6 Use the latest FDSI configurator, V1.4 #7 With the latest driver, configure all the diagnostic counter blocks for ECB200 and ECB201 These will help you determine the best TO= setting plus give a wealth of information on how the interface is performing. You could create a graphic with this information for easy access. #8 Determine if the RedLion is capable of Heartbeat and then determine which of the 3 heartbeat methods to use. #9 Kevin brought up a good point about having more than one Master on the bus at the same time and to know what exception codes are being returned from the PLC >> RedLion >> FBM230. Regards, Scott ________________________________________ From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Sandy AH [aloy_sah@xxxxxxxxx] Sent: Sunday, March 02, 2014 3:29 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley Dear Scott, Please find details in Blue as given below. Thanks and Regards, Sandy --------------------------------------------------------------------------------------------------------------------------------------- Please provide more background info; T/A switch settings, RS-232 settings matter even though you are using RS-485 Port-1 A B C 01 OPEN OPEN CLOSE 02 CLOSE CLOSE OPEN 03 OPEN OPEN OPEN 04 CLOSE CLOSE OPEN 05 CLOSE OPEN OPEN 06 OPEN OPEN OPEN 07 OPEN OPEN OPEN 08 OPEN CLOSE OPEN Port-2/3/4 ALL SWITCHES ARE IN CLOSE CONDITION T/A RS-485 termination setting ? Port-1/2/3/4 TX – OPEN RX - CLOSE FDSI driver type MODBUS.ZIPH FDSI driver revision 1.1 CRC F706988 FDSI firmware level SW: 1.31/0226 EEPROM: 0113/1.C7 FDSI port configuration settings Port : 1 Mode: RS485 Baud rate : 9600 Stop bit: 1 Databit: 8 Parity : None Driver: MODBUS/RTU+TO FDSI xml configuration (if used) PORT CONFIGURATION: Port : 1 Mode: RS485 Baud rate : 9600 Stop bit: 1 Data bit: 8 Parity : None Driver: MODBUS/RTU+TO DEVICE CONFIGURATION: DEFAULT SETTING FDSI ECB201 configuration DEVNAME: 1 DEVOPTS: MODBUS+TO 0 FILEID: OPV001DEV.XML How many DCI blocks (how many of each type and period/phase) RIN -43 & BIN – 24 (Phase -0 and Period – 2Sec) Allen-Bradley PLC Type Allen-Bradley L62 Processor Allen-Bradley PLC interface card to FDSI type Red lion (MODEL DSP - DATA STATION PLUS) Communications settings in interface card to FDSI Interface device communicating to AB PLC by using Ethernet communication and communicating to FBM230 by using RS485 Is your RS-485 loop properly terminated and grounded ? TXA and TXB properly terminated at both of ends. Grounding done at PLC Side Is your RS-485 loop properly installed and separated from EMI sources ? PLC cabinet is placed in the Field. This Cabinet is Purge protected and suitable for Zone-2 2A Did you configure any counter blocks for the ECB200 and ECB201(s) ? Not Configured ---------------------------------------------------------------------------------------------------------------------------------------------------------------------- On Saturday, March 1, 2014 5:50 PM, "Landry, Scott" <Scott.Landry@xxxxxxxxxxxx> wrote: Sandy, Please provide more background info; T/A switch settings, RS-232 settings matter even though you are using RS-485 T/A RS-485 termination setting ? FDSI driver type FDSI driver revision FDSI firmware level FDSI port configuration settings FDSI xml configuration (if used) FDSI ECB201 configuration How many DCI blocks (how many of each type and period/phase) Allen-Bradley PLC Type Allen-Bradley PLC interface card to FDSI type Communications settings in interface card to FDSI Is your RS-485 loop properly terminated and grounded ? Is your RS-485 loop properly installed and separated from EMI sources ? Did you configure any counter blocks for the ECB200 and ECB201(s) ? Regards, Scott ________________________________________ From: foxboro-bounce@xxxxxxxxxxxxx [foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of aloy_sah@xxxxxxxxx [aloy_sah@xxxxxxxxx] Sent: Saturday, March 01, 2014 1:12 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley Brian, I have tried to put 2 second, 30 second, timeout but the problem still persist. Once there is any break in the communication, then manually I have to disable then enable communication from SMDH. Regards, Sandy Sent from my Phone -----Original Message----- From: Brian Long <blong@xxxxxxx> Sender: foxboro-bounce@xxxxxxxxxxxxx Date: Fri, 28 Feb 2014 21:49:36 To: foxboro@xxxxxxxxxxxxx<foxboro@xxxxxxxxxxxxx> Reply-To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] FBM 230 RS-485 communication to Allen Bradley Probably need to add more time to timeout, see manual for details. Sorry to not be more help, I'm not close to any docs. Brian Sent from my iPad On Feb 28, 2014, at 9:24 PM, Sandy AH <aloy_sah@xxxxxxxxx> wrote: > Hi there, > I am interfacing FBM230 with PLC Allen Bradley over RS485. > The modbus data is Holding Register Floating Point (4 bytes) with all modbus > configuration as per the configuration in PLC. Everything is showing healthy > on communication and I can get the data in RIN and BIN blocks. > But after sometimes (let's say few hours) the communication fails (it shows > the device fail) and not automatically back to normal. I have to disable > communication and then enable communication in SMDH. Once I did this, the > communication immediately back to normal.� > For example if I disconnect the cable (RS485 cable) and connect it back, the > communication to PLC AB does not back to normal automatically, it requires me > to disable/enable communication in SMDH first in order to make the > communication back healthy. > Is there anyone can help on this since it is quite disturbing that I have to > disable / enable the communication every time there is a break in the > communication. > > Regards, > Sandy - QAFAC > > > _______________________________________________________________________ > This mailing list is neither sponsored nor endorsed by Invensys Process > Systems (formerly The Foxboro Company). Use the info you obtain here at > your own risks. Read http://www.thecassandraproject.org/disclaimer.html > > foxboro mailing list: //www.freelists.org/list/foxboro > to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join > to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave > _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave *** Confidentiality Notice: This e-mail, including any associated or attached files, is intended solely for the individual or entity to which it is addressed. This e-mail is confidential and may well also be legally privileged. If you have received it in error, you are on notice of its status. Please notify the sender immediately by reply e-mail and then delete this message from your system. Please do not copy it or use it for any purposes, or disclose its contents to any other person. This email comes from a division of the Invensys Group, owned by Invensys Limited, which is a company registered in England and Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 7AW (Registered number 166023). For a list of European legal entities within the Invensys Group, please select the Legal Entities link at invensys.com. Invensys Limited is owned by the Schneider-Electric Group. You may contact Invensys Limited on +44 (0)20 3155 1200 or e-mail reception@xxxxxxxxxxxx. This e-mail and any attachments thereto may be subject to the terms of any agreements between Invensys (and/or its subsidiaries and affiliates) and the recipient (and/or its subsidiaries and affiliates). _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave *** Confidentiality Notice: This e-mail, including any associated or attached files, is intended solely for the individual or entity to which it is addressed. This e-mail is confidential and may well also be legally privileged. If you have received it in error, you are on notice of its status. Please notify the sender immediately by reply e-mail and then delete this message from your system. Please do not copy it or use it for any purposes, or disclose its contents to any other person. This email comes from a division of the Invensys Group, owned by Invensys Limited, which is a company registered in England and Wales with its registered office at 3rd Floor, 40 Grosvenor Place, London, SW1X 7AW (Registered number 166023). For a list of European legal entities within the Invensys Group, please select the Legal Entities link at invensys.com. Invensys Limited is owned by the Schneider-Electric Group. You may contact Invensys Limited on +44 (0)20 3155 1200 or e-mail reception@xxxxxxxxxxxx. This e-mail and any attachments thereto may be subject to the terms of any agreements between Invensys (and/or its subsidiaries and affiliates) and the recipient (and/or its subsidiaries and affiliates). _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave