Chris, In a word, yes; it can be done. But in anther word, carefully - because an error can cost you big time depending on the risk assessment of your process. You could create something as simple as an ascii list of compounds and blocks to be cleared, then write a script or program that reads the C:B and then slowly (1 write per second) writes to the parameter to clear the alarm. You could run the script when the shutdown is happening (likely a manual pick by your Operator from a screen). You can maintain the ascii list with one C:B per line and add or delete C:B as required. If your instrument people delete a block, you need to be informed so that you can delete the line in the ascii file. Terry > Date: Fri, 16 Dec 2011 11:46:39 -0500 > Subject: [foxboro] Alarm Clearing > From: gooooomaker@xxxxxxxxx > To: foxboro@xxxxxxxxxxxxx > > All Knowing List- I am curious if anyone has had the need to allow > clearing of specific alarms and how you accomplished this. For example, we > have clearing disabled so we always have a list of active in- alarm's. In > a shutdown situation this may mask other alarms that may be more > important. Is there a way, via script or other programming, that I can > specify which alarms can be cleared and disable clearing on all others. > Thanks in advance, > > Chris _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave