Re: [foxboro] AW: AW: Foxboro and Allen Bradley, multiple PLCs

  • From: "Johnson, Alex (Foxboro)" <ajohnson@xxxxxxxxxxx>
  • To: foxboro@xxxxxxxxxxxxx
  • Date: Thu, 3 Jan 2002 08:52:22 -0500

What kind of PLC are you using and how do you make it look like a PROFIbus
device?


Regards,


Alex Johnson
System Products - Invensys Systems, Inc.
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
ajohnson@xxxxxxxxxxx <mailto:ajohnson@xxxxxxxxxxx> 



        -----Original Message-----
        From:   Maurer, Heinz [SMTP:hmaurer@xxxxxxxxxxx]
        Sent:   Thursday, January 03, 2002 2:15 AM
        To:     'foxboro@xxxxxxxxxxxxx'
        Subject:        [foxboro] AW: AW: Foxboro and Allen Bradley,
multiple PLCs


        Yes, up to 3 DP master in the micro are running well.

        Heinz Maurer

        Invensys Systems GmbH
        Vertriebsb=FCro D=FCsseldorf
        Heerdter Lohweg 53-55
        40549 D=FCsseldorf
                  Deutschland

        Tel.:     +49 (0) 211 5966 -333
        Fax.:    +49 (0) 211 5966 -300
        Mob.:   +49 (0) 173 25 32 515
        Email:   heinz.maurer@xxxxxxxxxxxx
        http://www.invensys-process-systems.de

        > -----Urspr=FCngliche Nachricht-----
        > Von:  Johnson, Alex (Foxboro) [SMTP:ajohnson@xxxxxxxxxxx]
        > Gesendet am:  Mittwoch, 2. Januar 2002 21:13
        > An:   foxboro@xxxxxxxxxxxxx
        > Betreff:      Re: [foxboro] AW: Foxboro and Allen Bradley,
multiple PLCs
        >=20
        >=20
        > Let's see if I understand what you are saying:
        >=20
        > *     Install one or more PROFIbus DP interface cards in the
Micro-I/A.
        > *     Connect the PLC as a PROFIbus slave device to the PROFIbus
network
        > *     Configure the Micro-I/A to read the PLC data as if it were
PROFIbus
        > data
        >=20
        > Is this correct?
        >=20
        >=20
        > Regards,
        >=20
        >=20
        > Alex Johnson
        > System Products - Invensys Systems, Inc.
        > 10707 Haddington
        > Houston, TX 77043
        > 713.722.2859 (office)
        > 713.722.2700 (switchboard)
        > 713.932.0222 (fax)
        > ajohnson@xxxxxxxxxxx <mailto:ajohnson@xxxxxxxxxxx>=20
        >=20
        >=20
        >=20
        >       -----Original Message-----
        >       From:   Maurer, Heinz [SMTP:hmaurer@xxxxxxxxxxx]
        >       Sent:   Wednesday, January 02, 2002 3:49 AM
        >       To:     'foxboro@xxxxxxxxxxxxx'
        >       Subject:        [foxboro] AW: Foxboro and Allen Bradley,
multiple
        > PLCs
        >=20
        >=20
        >=20
        >       Hi,
        >=20
        >=20
        >       if you want  to connect multiple PLCs to one Micro for
monitoring
        > and
        >       operating, you can use up to 3 profibus DP masters, each
with more
        > than =3D
        >       one
        >       client (PLC).
        >       We have experiences.
        >=20
        >=20
        >       Heinz Maurer
        >=20
        >       Invensys Systems GmbH
        >       Vertriebsb=3DFCro D=3DFCsseldorf
        >       Heerdter Lohweg 53-55
        >       40549 D=3DFCsseldorf
        >                 Deutschland
        >=20
        >       Tel.:     +49 (0) 211 5966 -333
        >       Fax.:    +49 (0) 211 5966 -300
        >       Mob.:   +49 (0) 173 25 32 515
        >       Email:   heinz.maurer@xxxxxxxxxxxx
        >       http://www.invensys-process-systems.de
        >=20
        >       > -----Urspr=3DFCngliche Nachricht-----
        >       > Von:  Johnson, Alex (Foxboro) [SMTP:ajohnson@xxxxxxxxxxx]
        >       > Gesendet am:  Freitag, 28. Dezember 2001 19:11
        >       > An:   foxboro@xxxxxxxxxxxxx
        >       > Betreff:      Re: [foxboro] Foxboro and Allen Bradley
        >       >=3D20
        >       >=3D20
        >       > The micro-I/A approach supports:
        >       >=3D20
        >       > *     One and only one PLC
        >       > *     Dual Nodebus interface
        >       > *     Single electronics
        >       >=3D20
        >       > If it were not for the limitation of support for one PLC
it would
        > be =3D
        >       a
        >       > very
        >       > nice solution.
        >       >=3D20
        >       >=3D20
        >       > Regards,
        >       >=3D20
        >       >=3D20
        >       > Alex Johnson
        >       > System Products - Invensys Systems, Inc.
        >       > 10707 Haddington
        >       > Houston, TX 77043
        >       > 713.722.2859 (office)
        >       > 713.722.2700 (switchboard)
        >       > 713.932.0222 (fax)
        >       > ajohnson@xxxxxxxxxxx <mailto:ajohnson@xxxxxxxxxxx>=3D20
        >       >=3D20
        >       >=3D20
        >       >       -----Original Message-----
        >       >       From:   Chris Browder [SMTP:chris_browder@xxxxxxxxx]
        >       >       Sent:   Friday, December 28, 2001 11:53 AM
        >       >       To:     foxboro@xxxxxxxxxxxxx
        >       >       Subject:        Re: [foxboro] Foxboro and Allen
Bradley
        >       >=3D20
        >       >=3D20
        >       >       Not much to add, but aren't there MicroIA solutions
        >       >       available that will connect via ethernet/ip to
PLC's?=3D20
        >       >       No one has mentioned them yet.  There was also some
        >       >       talk a while back about there being a redundant
option
        >       >       (in addition to fault tolerant) available in the
        >       >       future.
        >       >=3D20
        >       >       If available the MicroIA would then be used instead
of
        >       >       the AB30's...
        >       >=3D20
        >       >       chris.
        >       >=3D20
        >       >=3D20
        >       >       --- Rick de la Cierva <rcierva@xxxxxxxxxxxxxxxx>
        >       >       wrote:
        >       >       >=3D20
        >       >       > Bob,=3D3D20
        >       >       >=3D20
        >       >       > I think you caught many on vacation since this
topic
        >       >       > usually has many
        >       >       > interested subscribers willing to dive in. While I
        >       >       > was at lunch tough I
        >       >       > did see Joe provided some feedback also.
        >       >       >=3D20
        >       >       > The AB30 is a standard Foxboro module that can be
        >       >       > configured redundant.
        >       >       > One of the ports is configured to communicate to
the
        >       >       > CAM (see modules
        >       >       > listed below) that converts it to DH+. The
        >       >       > limitations are: "The Gateway
        >       >       > supports a maximum of 16 I/A Series Allen-Bradley
        >       >       > Scan Blocks (ABSCAN)
        >       >       > to perform input/output functions with up to eight
        >       >       > PLC controllers". I
        >       >       > believe these are not hard limitations but mostly
        >       >       > throughput limitations
        >       >       > one should follow. This module is basically just a
        >       >       > control processor 30
        >       >       > that can interface to PLCs. It only performs
control
        >       >       > functions.
        >       >       >=3D20
        >       >       > The Foxboro edocs indicate the interface modules
        >       >       > that can be used with
        >       >       > the the AB30 are " The Gateway interfaces to the
        >       >       > Allen-Bradley Data
        >       >       > Highway using 1771-KE/KF, 1770-KF2 Series B, or
        >       >       > 1779-KFL (in 1771-KE/KF
        >       >       > Emulation Mode) Communication Adapters". Note that
        >       >       > they are all for data
        >       >       > highway and not direct to ENET. I looked at the
        >       >       > information on the
        >       >       > 1761-NET-ENI and it seems like it should work also
        >       >       > but Rockwell has the
        >       >       > following note on their about this module: "Lets
you
        >       >       > connect MicroLogix
        >       >       > (or other products with an RS-232-C port and DF1
        >       >       > protocol) to an
        >       >       > EtherNet/IP network and initiate a single-hop
        >       >       > message with any
        >       >       > EtherNet/IP device via a connected CIP message.
        >       >       > Supports the NetLinx
        >       >       > services." - Note the single hop - I am not sure
how
        >       >       > your network looks.
        >       >       >=3D20
        >       >       > As Joe indicated, the other options to go directly
        >       >       > to the PLCs on
        >       >       > Ethernet is using either a 51 series(Solaris) or
70
        >       >       > series Integrator -
        >       >       > though these are not redundant. Basically these
are
        >       >       > either a Sun Box or
        >       >       > a Windows NT PC that run the Foxboro blocks inside
        >       >       > and connect to the
        >       >       > PLC directly on Ethernet. I have not tried the 70
        >       >       > series integrator but
        >       >       > have used the 51 series. On these AB Interchange
        >       >       > software is loaded and
        >       >       > is used to communicate to the PLCs. These also
have
        >       >       > a lot more
        >       >       > horsepower for blocks and your limitation is not
the
        >       >       > number of PLCs but
        >       >       > the throughput on the communication network and
the
        >       >       > ability of the PLC
        >       >       > to respond in adequate time. Since you mention the
        >       >       > AB30 module I am
        >       >       > guessing you have a typical Foxboro nodebus system
        >       >       > and not a standard
        >       >       > Ethernet system. You can add a second Ethernet
card
        >       >       > to these integrators
        >       >       > to connect them to the PLC Ethernet network and
        >       >       > connect the first
        >       >       > Ethernet to a DNBT cart so that the integrator is
        >       >       > also on your standard
        >       >       > Foxboro nodebus network.
        >       >       >=3D20
        >       >       > Give me a call if you want to discuss further.
        >       >       >=3D20
        >       >       > Rick de la Cierva
        >       >       > DLC SOLUTIONS CORP.
        >       >       > 203-207-9917
        >       >       >=3D20
        >       >       >=3D20
        >       >       > -----Original Message-----
        >       >       > From: Marchal, Andre L.
        >       >       > [mailto:AMarchal@xxxxxxxxxxxxxxx]=3D3D20
        >       >       > Sent: Friday, December 28, 2001 10:36 AM
        >       >       > To: 'foxboro@xxxxxxxxxxxxx'
        >       >       > Subject: Re: [foxboro] Foxboro and Allen Bradley
        >       >       >=3D20
        >       >       >=3D20
        >       >       > Bob,
        >       >       >=3D20
        >       >       > I also tried to connect an INT30 to Allen Bradley
        >       >       > 5/40E's without =3D3D3D
        >       >       > success.
        >       >       > I used an 1761-NET-ENI to do the
DF1-RS232/Ethernet
        >       >       > conversion.
        >       >       > I do not know what the problem was (improper
wiring,
        >       >       > protocol, etc...).
        >       >       > Please let me know if you find a successful
method.
        >       >       >=3D20
        >       >       > Bob, this is what I understand:  the INT30 for
Allen
        >       >       > Bradley can =3D3D3D
        >       >       > communicate
        >       >       > with up to 8 PLCs.  It has 2 redundant RS232 ports
        >       >       > (that is a powerful =3D3D
        >       >       > =3D3D3D
        >       >       > and
        >       >       > easy to use feature).  If you want to communicate
        >       >       > with more PLCs, you =3D3D
        >       >       > =3D3D3D
        >       >       > would
        >       >       > have to use one of the configured PLCs as a "mail
        >       >       > box".
        >       >       >=3D20
        >       >       > Here is what I used for my test:
        >       >       > INT30=3D3D3D20
        >       >       > SCSI cable P0500UX
        >       >       > Serial connector P0970VB
        >       >       > Ethernet interface 1761-NET-ENI (Allen Bradley)
        >       >       > Serial cable 1761-CBL-PM02 (Allen Bradley)
        >       >       >=3D20
        >       >       > Andr=3D3D3DE9 Marchal
        >       >       > -----Original Message-----
        >       >       > From: Robert Driscoll [mailto:rdrisco@xxxxxxxxxxx]
        >       >       > Sent: Friday, December 28, 2001 7:55 AM
        >       >       > To: foxboro@xxxxxxxxxxxxx
        >       >       > Subject: [foxboro] Foxboro and Allen Bradley
        >       >       >=3D20
        >       >       >=3D20
        >       >       >=3D20
        >       >       > Hello List,
        >       >       >=3D20
        >       >       > I am installing several Allen Bradley PLCs and I
        >       >       > want to connect them =3D3D
        >       >       > =3D3D3D
        >       >       > to a=3D3D3D20
        >       >       > Foxboro system.  I know a few things about the
        >       >       > Foxboro hardware but I =3D3D
        >       >       > =3D3D3D
        >       >       > have a
        >       >       >=3D20
        >       >       > few questions.
        >       >       >=3D20
        >       >       > How many PLCs can a single AB30 module be directly
        >       >       > connected to?  The =3D3D
        >       >       > =3D3D3D
        >       >       > module
        >       >       >=3D20
        >       >       > has four ports, so I assume it can go to four
        >       >       > different PLCs?
        >       >       >=3D20
        >       >       > I read the Foxboro on-line document and it
discussed
        >       >       > the RS232 =3D3D
        >       >       > direct=3D3D3D20
        >       >       > connection to a PLC, or a connection through a
CAM.=3D20
        >       >       > My PLCs will =3D3D
        >       >       > be=3D3D3D20
        >       >       > networked together through a hub.  Is there a
        >       >       > Foxboro way of =3D3D3D
        >       >       > communicating=3D3D3D20
        >       >       > to the PLCs via ETHERNET?  I could not find that
in
        >       >       > the
        >       >       > documentation.  Is it possible to connect the Fox
        >       >       > module(s) into the =3D3D3D
        >       >       > hub and
        >       >       >=3D20
        >       >       > have the devices talk that way?
        >       >       >=3D20
        >       >       > Any other pitfalls with the AB30 (or other modules
        >       >       > that may apply =3D3D3D
        >       >       > here)?
        >       >       >=3D20
        >       >       > Bob Driscoll
        >       >       > Bravo Northwest Power Systems
        >       >       >=3D20
        >       >       >=3D20
        >       >       >=3D20
        >       >       >
        >       >
        > _________________________________________________________________
        >       >       > Join the world's largest e-mail service with MSN
        >       >       > Hotmail.=3D3D3D20
        >       >       > http://www.hotmail.com
        >       >       >=3D20
        >       >       > =3D3D3D20
        >       >       > =3D3D3D20
        >       >       >
        >       >
        >
___________________________________________________________________
        >       >       > This list is neither sponsored nor endorsed by The
        >       >       > Foxboro Company.
        >       >       > Use the information obtained here at your own
risk.
        >       >       > For disclaimer,
        >       >       > see
        >       >       >
        >       >
http://www.thecassandraproject.org/disclaimer.html#maillist
        >       >       >=3D20
        >       >       > list info:   //www.freelists.org/list/foxboro
        >       >       > subscribe: =3D20
        >       >       >
        >       >
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3Djoin
        >       >       > unsubscribe:
        >       >       >
        >       >
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3D3Dleave
        >       >       >=3D20
        >       >       =3D3D=3D3D=3D3D message truncated =3D3D=3D3D=3D3D
        >       >=3D20
        >       >=3D20
        >       >       __________________________________________________
        >       >       Do You Yahoo!?
        >       >       Send your FREE holiday greetings online!
        >       >       http://greetings.yahoo.com
        >       >       =3D20
        >       >       =3D20
        >       >
        >
___________________________________________________________________
        >       >       This list is neither sponsored nor endorsed by The
Foxboro
        > Company.
        >       >       Use the information obtained here at your own risk.
For
        > disclaimer,
        >       >       see
        > http://www.thecassandraproject.org/disclaimer.html#maillist
        >       >=3D20
        >       >       list info:   //www.freelists.org/list/foxboro
        >       >       subscribe:
        > mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin
        >       >       unsubscribe:
        > mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave
        >       > =3D20
        >       > =3D20
        >       >
        >
___________________________________________________________________
        >       > This list is neither sponsored nor endorsed by The Foxboro
        > Company.
        >       > Use the information obtained here at your own risk. For
        > disclaimer,
        >       > see
http://www.thecassandraproject.org/disclaimer.html#maillist
        >       >=3D20
        >       > list info:   //www.freelists.org/list/foxboro
        >       > subscribe:
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin
        >       > unsubscribe: =
        mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave
        >       =20
        >       =20
        >
___________________________________________________________________
        >       This list is neither sponsored nor endorsed by The Foxboro
Company.
        >       Use the information obtained here at your own risk. For
disclaimer,
        >       see
http://www.thecassandraproject.org/disclaimer.html#maillist
        >=20
        >       list info:   //www.freelists.org/list/foxboro
        >       subscribe:
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
        >       unsubscribe:
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
        > =20
        > =20
        >
___________________________________________________________________
        > This list is neither sponsored nor endorsed by The Foxboro
Company.
        > Use the information obtained here at your own risk. For
disclaimer,
        > see http://www.thecassandraproject.org/disclaimer.html#maillist
        >=20
        > list info:   //www.freelists.org/list/foxboro
        > subscribe:   mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
        > unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
         
         
        ___________________________________________________________________
        This list is neither sponsored nor endorsed by The Foxboro Company.
        Use the information obtained here at your own risk. For disclaimer,
        see http://www.thecassandraproject.org/disclaimer.html#maillist

        list info:   //www.freelists.org/list/foxboro
        subscribe:   mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
        unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 
 
___________________________________________________________________
This list is neither sponsored nor endorsed by The Foxboro Company.
Use the information obtained here at your own risk. For disclaimer,
see http://www.thecassandraproject.org/disclaimer.html#maillist

list info:   //www.freelists.org/list/foxboro
subscribe:   mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave

Other related posts:

  • » Re: [foxboro] AW: AW: Foxboro and Allen Bradley, multiple PLCs