Bert,
Sorry, I'm not following... You previously mentioned that only one GND
exists in a system. Is there any connection between this GND and Chassis
GND?

Lee - by "card cage" do you mean the chassis itself?

On Sat, Jan 7, 2017 at 9:30 PM, Bert Simonovich <bertsimonovich@xxxxxxxxxx>
wrote:

Boris,

It isn't any different. The actual "Chassis Gnd" of the shelf is connected
to the frame or rack which is connected to the IBN of CBN of the facility
which is effectivly "earth gnd".

------------------------------
*From:* Boris Bakshan [mailto:bbakshan@xxxxxxxxx]
*Sent:* 7-Jan-17 2:03 PM
*To:* bertsimonovich@xxxxxxxxxx
*Cc:* Lee Ritchey; si-list
*Subject:* Re: [SI-LIST] Re: An Article on what ground is

Hi Bert, Lee,

This makes completely sense.
However, as with any commercial electronic device that has a metallic
enclosure (VCR, amplifiers, multimedia boxes, etc') connected to
Earth/Safety ground via third contact in a power cord, I would expect the
same thing with a Shelf/Chassis. Why should this be different ? For safety
reasons, why shouldn't the (conductive) body of any chassis be connected to
earth ground?

Thanks.



On Sat, Jan 7, 2017 at 8:54 PM, Bert Simonovich <bertsimonovich@xxxxxxxxxx
wrote:

Boris,

I have done essentially the same thing Lee has described in all of the
backplanes I have designed in the past, except that in our case the outer
PCB layers on both sides were "GND" plane, and the PCB was edge plated.
This
created a faraday shield for all the internal layers. The backplane was
metalically connected to the shelf framework with screws without
isolation.
There was only one "GND" in the system, including the line cards that
plugged into the shelves.

This "grounding" scheme was compatible with single-point ground/integrated
bonding network (SPG/IBN) and mesh/common bonding network(Mesh/CBN). Our
systems had to meet  GR-1089-CORE - Electromagnetic compatibility and
electrical safety for network telecommunications equipment.

-48V Battery and Battery return powering the system was isolated from the
"Chassis GND" with an option to join the battery return to "chassis
ground"
at the single power entry point.

Regards,

Bert Simonovich
Signal/Power Integrity Practitioner | Backplane Specialist | Founder
LAMSIM Enterprises Inc.
Web Site: http://lamsimenterprises.com
Blog: http://blog.lamsimenterprises.com/

-----Original Message-----
From: si-list-bounce@xxxxxxxxxxxxx [mailto:si-list-bounce@xxxxxxxxxxxxx]
On
Behalf Of Boris Bakshan
Sent: 7-Jan-17 1:16 PM
To: Lee Ritchey
Cc: si-list
Subject: [SI-LIST] Re: An Article on what ground is

Hi Lee,
Thank you for prompt reply.
So, in fact, you are making a direct connection between the logic ground
of
the cards and the metalic chassis enclosure so that backplane ground
(return
path of signals) , cards logic ground and metalic chassis enclosure are
all
connected, did I get it right?

On Jan 7, 2017 7:57 PM, "Lee Ritchey" <leeritchey@xxxxxxxxxxxxx> wrote:

Thanks for the nice feedback.

Aha!  You have asked an EMI question!  I use the ground plane in a
backplane as one side of my Faraday cage.  Where that backplane meets
the flanges on the card cage, I leave the copper on the top layer and
connect that with vias to the ground plane in the backplane.  Now,
there is the one connection between logic ground and the Faraday cage.
There can be no other connections such as on face places if one is to
avoid "leaking" at the cracks which is a common complaint when more
than one connection is made between logic ground and the Faraday cage.
Notice, I did not use the phrase "chassis ground" in this discussion.

I have used this method in dozens of systems with very good EMI results.

Hope this helps.

Lee

-----Original Message-----
From: si-list-bounce@xxxxxxxxxxxxx
[mailto:si-list-bounce@xxxxxxxxxxxxx]
On
Behalf Of Boris Bakshan
Sent: Saturday, January 7, 2017 5:24 AM
To: Lee Ritchey <leeritchey@xxxxxxxxxxxxx>
Cc: si-list <si-list@xxxxxxxxxxxxx>
Subject: [SI-LIST] Re: An Article on what ground is

Hi Lee,
Very good, comprehensive article, thank you.
What is your recommendation when it comes to backplanes? a backplane
is attached to the chassis with bolts/other conductive mechanical
parts. Do you recommend plating these PCB holes in the backplane? If
you do, should these holes be connected to (any) electrical net?

Thanks Lee.


On Fri, Jan 6, 2017 at 10:43 PM, Lee Ritchey
<leeritchey@xxxxxxxxxxxxx>
wrote:

I have written an article on ground following the brisk exchange on
this subject last month.  I hope it clears up some of the confusion
around this subject.


Here is where it is on the web.



http://ubm.io/2ikEDat



Lee Ritchey

Speeding Edge

P.O. Box 2194

Glen Ellen, CA

95442

707-568-3983



I just used the energy it takes

To get mad and wrote some blues.

Count Basie



Or:

Worry is like a rocking chair,

It keeps you busy but.

It doesn't get you anywhere.





------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject
field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
               http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
                //www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu





------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
               http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
                //www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu





------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
               http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:
                //www.freelists.org/archives/si-list

Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu


-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2016.0.7996 / Virus Database: 4749/13724 - Release Date: 01/07/17


------------------------------

No virus found in this message.
Checked by AVG - www.avg.com <http://www.avg.com/email-signature>
Version: 2016.0.7996 / Virus Database: 4749/13724 - Release Date: 01/07/17



------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field


List forum  is accessible at:
               http://tech.groups.yahoo.com/group/si-list

List archives are viewable at:     
                //www.freelists.org/archives/si-list
 
Old (prior to June 6, 2001) list archives are viewable at:
                http://www.qsl.net/wb6tpu
  

Other related posts: