Matt, You might want to ignore IDLE time for the CP's. You do not see the = total of CPLOAD + IDLE =3D 100 very often. =20 Guidelines recommend 60 max for Fieldbus load and 80 Max for Total = CPLOAD. If you can get to these values, you should be OK. But the real truth lies in CP overruns. You really want the integrator = reading zero at all times. Maybe if you are doing an engineering = function like ICC and you exit which causes a CHECKPOINT you could allow = a count or two on the overrun. You can grab the CP60 loading spreadsheet (Excel) from EDOC or the Fox Web site if you have a contract. The Excel will allow you to do a=20 "what if" analysis without actually changing block periods or phases in = the CP60 until the Excel says your loading is OK. The Excel for CP60 should be pretty darn close to what you see in the = running CP. If you have a lot of sequence blocks you might have to play = with the Excel defaults. If you slow down all blocks on a particular input IO card, you should = actually change the period of the corresponding ECB so that the IO = integration period matches your AIN period. Try to eliminate aliasing. If you phase your control loops (AIN, PIDA, AOUT) watch that you do not = accidentally change the order of block processing and add an extra = period of delay. The OM overruns are a different matter. If you have no peer connections = for control loops or shutdown control, you may be able to accept a few = OM overruns per day. This usually means a delay in Historian receiving = data changes or CRT screens being delayed in their updates. In most CP's = the OM overrun is less critical. But there may be cases where OM = overruns are totally unacceptable, too. Terry -----Message d'origine----- De=A0: foxboro-bounce@xxxxxxxxxxxxx = [mailto:foxboro-bounce@xxxxxxxxxxxxx] De la part de Gunter, Matt Envoy=E9=A0: 11 octobre 2007 11:08 =C0=A0: foxboro@xxxxxxxxxxxxx Objet=A0: Re: [foxboro] Timer Question MeeOuch! As Spencer Katt of eWeek would say! Thanks to everyone for their comments. We are running CP60s and I have suspected loading. Here's the skinny ... CP Field Bus Scan Cont Blks Seq Blks Total Station Idle Good Timer CP 61.4 13.4 3.2 78.0 62.9 Bad Timer CP 1 121.2 15.8 7.6 144.6 77.6 Bad Timer CP 2 114.8 13.0 6.0 133.8 80.4 When I check the loading in our lab, the field bus scan is zero - of course since it is not hooked to any real hardware. Apparently the higher station idle time is not indicative of resources available to process timer blocks. It appears that I am going to have to figure out a way to reduce field bus scanning. Best Regards Matt Gunter ATK Launch Systems -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Johnson, Alex P (IPS) Sent: Tuesday, October 09, 2007 10:37 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Timer Question It was corrected for the ACCUM block some time ago; I can't remember the release. Regards, Alex Johnson Invensys Systems, Inc. 10900 Equity Drive Houston, TX 77041 713.329.8472 (voice) 713.329.1700 (fax) 713.329.1600 (switchboard) alex.johnson@xxxxxxxxxxxxxxxx -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Douglas G. Lloyd Sent: Tuesday, October 09, 2007 5:42 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Timer Question Hi All, The CP overrun time loss issue used to affect all blocks that have time based algorithms (TIM, ACCUM, RAMP, CALC family, PID family, etc). CP overruns are much less of an issue with the latest processors, but it would be interesting to know if this problem has actually been corrected. Does anyone know for sure?? Regards, Doug DGL Controls -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Johnson, Alex P (IPS) Sent: Tuesday, October 09, 2007 2:15 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Timer Question All blocks are processed without exception - today. This was not the case in very early versions of the I/A Series. If you have a Y2K compliant version, all blocks will run. The BPC will be extended (typically doubled) and the left over time in the new, improved (longer) BPC is used for overheads. This behavior allows the CP to degrade gracefully under overload situations, but does impact timers. The ACCUM blocks suffered this problem through many releases, but I believe that it has been corrected to use the current reading for the previously missed cycles as a better estimate than ignoring the cycle. Regards, Alex Johnson Invensys Systems, Inc. 10900 Equity Drive Houston, TX 77041 713.329.8472 (voice) 713.329.1700 (fax) 713.329.1600 (switchboard) alex.johnson@xxxxxxxxxxxxxxxx -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Kevin Fitzgerrell Sent: Tuesday, October 09, 2007 4:30 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Timer Question Ken, Sorry, I missed your point before. Does this mean that TIM blocks are processed in an extended BPC while other blocks in the same overloaded CP may be processed in an overrun? My understanding was that in a control station, all blocks were processed without exception, the BPC overrunning to allow that. Seems a bit odd if the TIM blocks are treated differently, as that could change the normal compound/block processing order. Which manual was that quote from? Regards, Kevin FitzGerrell On 10/9/07, Kevin_Fitzgerrell@xxxxxxx <Kevin_Fitzgerrell@xxxxxxx> wrote: > Ken, > > While the TIM blocks are always processed, the next cycle is delayed if > overloaded. The timing on the TIM blocks depends on each block=3D20 > executing in it's scheduled slot. So, although the TIM blocks = are=3D20 > always executed, the extra overrun slots in between the normal = block=3D20 > execution slots affects the timing. This also affects ACCUM blocks and > I believe CALC block timing (DON, DOFF, etc). > > Kevin > > -----Original Message----- > =3D3D3D3D46rom: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] > On Behalf Of Moore, Kenneth, Celanese/US > Sent: Tuesday, October 09, 2007 6:31 AM > To: foxboro@xxxxxxxxxxxxx > Subject: Re: [foxboro] Timer Question > > > I'm looking at an old block book, but the last entry is a Note that > states: > "In a serious system overload, TIM blocks are always processed, even if > it delays the next BPC". > > So if you seriously overloaded, every additional TIM block added to the > system extends the BPC. > > > > Ken Moore > Celanese > Enoree SC > =3D3D =3D3D _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D3D foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3Djoin to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3D3Dleave =3D3D Confidentiality Notice: This e-mail and any associated files are intended solely for the individual=3D3D or entity to whom they are addressed. Please do not = copy =3D it or use it for =3D3D any purposes, or disclose its contents to any other person. Further, this e=3D3D -mail and any associated files may be confidential and further may be legal=3D3D ly privileged. This email is = =3D from the Invensys Process Systems business uni=3D3D t of Invensys plc which = is =3D a company registered in England and Wales with i=3D3D ts registered office = =3D at Portland House, Bressenden Place, London, SW1E 5BF =3D3D (Registered =3D number 166023). For a list of European legal entities within t=3D3D he = Invensys Process Systems business group, please click here http://www.in=3D3D vensys.com/legal/default.asp?top_nav_id=3D3D3D77&nav_id=3D3D3D80&prev_id=3D= 3D3D=3D 77. If you have received this e-mail in error, you are on notice of its status.=3D3D Please notify us immediately by reply e-mail and then = delete this message =3D3D from your system. Thank you for your co-operation. = You may contact our Help=3D3D desk on +44 (0)20 7821 3859 / 2105 or email inet.hqhelpdesk@xxxxxxxxxxxxx T=3D3D his e-mail and any attachments =3D thereto may be subject to the terms of any a=3D3D greements between Invensys =3D (and/or its subsidiaries and affiliates) and the=3D3D recipient (and/or its subsidiaries and affiliates). =3D20 =3D20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin to unsubscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave =3D20 =20 =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin to unsubscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave