Note, at least with a V7.X/V6.X Unix mixed system (except for 2 AW70 OPC
gateways), a similar problem also occurs when you eliminate alarms by
changing the hex address to 0 for the Station Block Alarm Group assignments
in ICC.  To get the alarm groups to work again (i.e. report alarms to the
WPs, etc.) later as they originally did, you have to enter the same hex
address and then pick on each of the alarm devices in the Station Block
(that were never removed from the list) and hit the enter key, before
hitting the DONE button in ICC.



Neil Martin
Huntsman Performance Chemicals



                                                                           
             "Ron Schafer"                                                 
             <rschafer@xxxxxxx                                             
             ebirchpaper.com>                                           To 
             Sent by:                  <foxboro@xxxxxxxxxxxxx>             
             foxboro-bounce@fr                                          cc 
             eelists.org                                                   
                                                                   Subject 
                                       Re: [foxboro] Station Block group   
             08/27/2007 02:32          assignments                         
             PM                                                            
                                                                           
                                                                           
             Please respond to                                             
             foxboro@freelists                                             
                   .org                                                    
                                                                           
                                                                           




We had the same problem at 6.3 and had whitespaces after the names. The
solutions was:
I believe you need to enter your devices by selecting from ICC SHOW ->
AVAILABLE WP's and then select the desired station and confirm with
Enter
key.

Then I found the whitespace issue.

Ronald G. Schafer
10026 Old Ridge Rd.
Ashland Va. 23009
804-227-4034
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Pat Martens
Sent: Monday, August 27, 2007 2:47 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Station Block group assignments



Would not know if it is still the case with 6.5.4 but we had similar
problems with 6.3.

I believe you need to enter your devices by selecting from ICC SHOW ->
AVAILABLE WP's and then select the desired station and confirm with
Enter
key.
Typing or setting with icc script could give unpredictable results.

Kind regards,
Patrick Martens

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On
Behalf Of Goldie, Shaun S
Sent: maandag 27 augustus 2007 20:35
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Station Block group assignments

Hi
I am looking for an explanation for a bit of a hole we dug ourselves
into.
The job was to move a CP60 eeprom and load a new OS version
To prevent the operators from getting all the alarms reissued (twice) we
took the operator workstations out of the station groups did the job and
reinstated the station groups.
It was into plant startup that we realised the workstations were not
getting alarms from that CP. With a CP reboot not possible we tried
Workstation reboot & Reentering group assignments of 0 checkpoint then
enter the correct value
Which didn't make any difference
What worked for us was change all the device names to a device that was
working (we never reassigned our engineering station so it kept working)
and generate an alarm for each group then change the device names back

? relevance but Solaris 6.5.4 and the CP60 6.5.5b QF1008936
Shaun


=0A=0ANOTICE - This message and any attached files may contain
informatio=
n that is confidential and intended only for use by the intended
recipien=
t. If you are not the intended recipient or the person responsible for
de=
livering the message to the intended recipient, be advised that you have
=
received this message in error and that any dissemination, copying or
use=
 of this message or attachment is strictly forbidden, as is the
disclosur=
e of the information therein. If you have received this message in error
=
please notify the sender immediately and delete the message.


_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave




_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


-- No attachments (even text) are allowed --
-- Type: text/x-vcard
-- File: rschafer@xxxxxxxxxxxxxxxxxxxxxxxxxx
-- Desc: rschafer@xxxxxxxxxxxxxxxxxxxxxxxxxx




_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: