Mike,

Sorry I don't have a better answer, but I tested the following calc with a PID
and it does what I think you need.

Regards,
Jason Wright
Invensys/Foxboro

where:
RI01 -> connected from .SPT of controller
RI02 -> desired RSP when machine is down
BI01 -> LR set by logic
RO01 -> connected to .RSP of controller
BO01 -> connected to .LR of controller

STEP01 BII 33  ; Initialize block if first use
STEP02 IN M01 ; Previous LR command
STEP03 IN BI01 ; Current LR command
STEP04 SUB  ; Compare
STEP05 BIZ 7  ; If same, do nothing
STEP06 GTO 10 ; If different, perform required action
STEP07 EXIT   ; exit

STEP10 IN BI01 ; LR command
STEP11 BIT 24; If Remote, go to remote logic

STEP13 NOP; Set-to-Local Logic
STEP14 IN M02 ; Stored SPT
STEP15 OUT RO01 ; RSP of controller
STEP16 IN RI01 ; Current SPT
STEP17 SUB  ; Compare
STEP18 BIZ 20 ; If same continue
STEP19 EXIT ; If not, exit
STEP20 STM M01 ; Store LR Command as previous (0)
STEP21 CLR BO01 ; Set LR to 0
STEP22 EXIT

STEP24 NOP; Set-to-Remote Logic
STEP25 STM M01; Store LR Command as previous
STEP26 IN RI01 ; Get SPT
STEP27 STM M02 ; Store to memory
STEP28 IN RI02 ; Get Desired RSP
STEP29 OUT RO01 ; Set RSP
STEP30 SET BO01; Set LR to 1
STEP31 EXIT

STEP33 NOP; Initialization logic
STEP34 IN ~BI01 ; Get inverse of LR command
STEP35 STM M01 ; Store as previous to force logic to run
STEP36 IN RI01 ; Get current SPT
STEP37 STM M02; Store as previous
STEP38 END

Mike Pauley wrote:

> Yes they know . This would happens while Paper Machine goes down for what
> ever reason.
> The shower water temperature runs with a setpoint of 55 degC . When they go
> down the setpoint
> changes to 35 degC. When they go back up they want the controller back to
> local and a setpoint
> back to value before break or shutdown. The way it works now, the
> controller stays in remote all
> the time and the setpoint switches from 35 degC and a remote transmitter.
> The remote transmitter
> is being removed.
>       Regards Mike
>
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list:             //www.freelists.org/list/foxboro
> to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: