Corry, We have experience similar "infant mortality" problems with FBM214 TA's during recent commissioning. I believe we had 2 such failures. None since. Technician wrote up the below technote capture for future diagnostics of similar occurrences in house. During Foxboro Controls installation and testing, we experienced loss of control on a piece of equipment utilizing 4-20ma current loop of an FBM214. Hart communication in this instance is only utilized for a feedback indication. Upon discovery of this malfunction, we replaced the suspected FBM module with a new one with no change of symptoms noted. Further investigation led us to suspect that the problem was in the FBM214 Termination Assembly. Utilizing a digital ohmmeter, we checked the resistance readings across terminals ?A? and ?C? of each input. It was discovered that the input in question read approximately 80K-120K Ohms, as compared to a normal reading of 8+Megohms on known good inputs. Readings were taken with the module deenergized and field wiring lifted. We then replaced the TA, and the problem was solved. We have experience other HART FBM issues as well. Most recently, last week we encountered issue where ALL CURRENT values from a FBM 214 ( EEPROM version 2.40D ) experienced an abrupt gain across all channels of approximately 20-30 percent. Foxboro TAC told us that this was a known issue ( No technical advisory bulletin ever issued??????) A EEPROM new EEPROM update was released on Friday last week (QF1013828) that is supposed to partially address the issue. They still don't know, and I don't believe have been able to replicate the problem in house, but this has occurred at 4 customer sites. This could have been a very catastrophic event, but fortunately, our IO and logic was partitioned and segmented in such a way that disaster was averted. We exclusively use CURRENT from the HART channels for control. Do not poll HART signals. for RIN's. We do use RIN HART PV signals against our 215 hart AO's for deviation alarm purposes though. During the HART AI gain event, the HART PV signal was unaffected, as confirmed at the transmitter, via 375 hand held, and by PACWare interrogation. Scary to say the least. I would be interested to lean who the other customers were that experienced this A/D Gain, and how their systems were affected. And why an advisory bulletin was never issued. Foxboro?? Sheldon Smith Office:972-884-2843 Cell: 214-460-4073 EFax: 866-734-2905 Conf: 877-253-4307 #7082843 Mailto: sssmith1@xxxxxxx _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave