Corry,
We have experience similar "infant mortality" problems with FBM214 TA's 
during recent commissioning.   I believe we had 2 such failures.  None 
since.
Technician wrote up the below technote capture for future diagnostics of 
similar occurrences in house.
During Foxboro Controls installation and testing, we experienced loss of 
control on a piece of equipment utilizing 4-20ma current loop of an 
FBM214. Hart communication in this instance is only utilized for a 
feedback indication. Upon discovery of this malfunction, we replaced the 
suspected FBM module with a new one with no change of symptoms noted. 
Further investigation led us to suspect that the problem was in the FBM214 
Termination Assembly. Utilizing a digital ohmmeter, we checked the 
resistance readings across terminals ?A? and ?C? of each input. It was 
discovered that the input in question read approximately 80K-120K Ohms, as 
compared to a normal reading of 8+Megohms on known good inputs. Readings 
were taken with the module deenergized and field wiring lifted. We then 
replaced the TA, and the problem was solved. 


We have experience other HART FBM issues as well.
Most recently, last week we encountered issue where ALL CURRENT values 
from a FBM 214 ( EEPROM version 2.40D ) experienced an abrupt gain across 
all channels of approximately 20-30 percent.
Foxboro TAC told us that this was a known issue ( No technical advisory 
bulletin ever issued??????)
A EEPROM new EEPROM update was released on Friday last week  (QF1013828) 
that is supposed to partially address the issue.   They still don't know, 
and I don't believe have been able to replicate the problem in house, but 
this has occurred at 4 customer sites.   This could have been a very 
catastrophic event, but fortunately, our IO and logic was partitioned and 
segmented in such a way that disaster was averted.


We exclusively use CURRENT from the HART channels for control.   Do not 
poll HART signals. for RIN's.   We do use RIN HART PV signals against our 
215 hart AO's for deviation alarm purposes though.

During the HART AI gain event, the HART PV signal was unaffected, as 
confirmed at the transmitter, via 375 hand held, and by PACWare 
interrogation.
Scary to say the least.

 
I would be interested to lean who the other customers were that 
experienced this A/D Gain, and how their systems were affected.   And why 
an advisory bulletin was never issued.
Foxboro?? 
















Sheldon Smith 
Office:972-884-2843
Cell:   214-460-4073 
EFax:   866-734-2905
Conf:  877-253-4307 #7082843
Mailto: sssmith1@xxxxxxx
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: