Thanks Chuck, Our BMS has to comply with NFPA8502. Hence if we were to change the = PLC5's we would require another redundant CP60 pair and I/O. This is the = preferred solution from the engineering point of view as with this = solution the system would be almost identical to two other retrofits = that were performed previously at our plant. The constraint however is budget. This in addition to the fact that the = BMS works reasonably well are the reasons why we would be keeping the = PLC's. The problems with the PLC have been - troubleshooting, alarm management = & historical data. This we intend to solve with the I/A system = integration. I will look into the gateway solution. Thanks. NB. -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]On Behalf Of Jones, Charles R. (Chuck) Sent: Monday, May 23, 2005 5:16 PM To: 'foxboro@xxxxxxxxxxxxx' Subject: Re: [foxboro] Foxboro I/A interface with PLC5/30's I recommend clearly defining the separation between the PLC and I/A very = for a couple of reasons. One reason is to lower the amount of information = that needs to pass between them to the smallest amount necessary. If you can define the BMS down to a "black box" you may treat it similarly to a = motor -- Turn ON, Turn OFF, Let me know if there is a problem, etc. =20 The other reason is to comply with safety regulatory agencies. I = recommend keeping the BMS as self-contained as possible, but the regulations in = your area may be different than mine. (And, if the current BMS works, why = fix it?) Lowering the amount of communication between I/A and burner = management makes it easier to certify for safety--and to troubleshoot, later on. Our equipment is older than you have to work with. We have redundant = CP30s and AP51As. We use an AB Gateway. The basic processing cycle is 2 = seconds. So, our BMSs have to be self-contained to be fast enough. But, the = combined system works just fine. Once you have clearly defined what each processor will do, the = communication solution will depend on how much data you actually need to pass between = I/A and PLC (and to how many PLCs you must communicate). Chuck Jones Refinery Automation Technologist Tate & Lyle -- Lafayette South Plant 765.477.5324 - Office | 877.536.9219 - Pager -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] = On Behalf Of Baptiste, Nigel Sent: Monday, May 23, 2005 3:21 PM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Foxboro I/A interface with PLC5/30's Thanks Chuck. The I/A system (Unix based) will be doing the boiler combustion controls = =3D and motor control as well as data acquisition. The project is still in the planning stages so I am seeking advice on = =3D how to proceed. We can do either of your options but I would like to =3D know which is your recommendation based on your experience. NB. -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]On Behalf Of Jones, Charles R. (Chuck) Sent: Monday, May 23, 2005 4:12 PM To: 'foxboro@xxxxxxxxxxxxx' Subject: Re: [foxboro] Foxboro I/A interface with PLC5/30's I've done this and I'm sorry to hear about your troubles... But =3D seriously, now it's not as bad as it once was. Before we can begin to send you advice, can you let us know whether you = =3D are running on Unix or Windows? =3D20 And, will your I/A system primarily supply the user interface or will = =3D there be controls as well? =3D20 Or, better yet (since the PLC is only for BMS), can you focus your I/A = =3D to AB interface down to passing a few digital bits of information back and =3D forth? Is it good enough that the I/A can just say, "Turn ON (or OFF) the =3D flame" and is it okay if the I/A only has to know whether the flame is ON or = =3D OFF? Chuck Jones Refinery Automation Technologist Tate & Lyle -- Lafayette South Plant 765.477.5324 - Office | 877.536.9219 - Pager -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] = =3D On Behalf Of Baptiste, Nigel Sent: Monday, May 23, 2005 2:59 PM To: foxboro@xxxxxxxxxxxxx Subject: [foxboro] Foxboro I/A interface with PLC5/30's Hello list, Does anyone have experience interfacing I/A with AB PLC5/30's? I have to integrate the two for combustion control & burner management = =3D =3D3D on a steam turbine generator unit. The combustion controls would be replaced with the I/A system but the = =3D =3D3D budget does not permit the replacement of the PLC based BMS. Hence I'm seeking the best way to interface the two systems. Regards, Nigel Baptiste. =3D20 =3D20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin to unsubscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave =3D20 *************************************************************************= =3D **************************** This email and any files transmitted with it are confidential and =3D intended solely for the=3D20 use of the individual or entity to whom they are addressed. If you are = =3D not the intended=3D20 recipient or the person responsible for delivering the email to the =3D intended recipient, be=3D20 advised that you have received this email in error that any use, =3D dissemination,=3D20 forwarding, printing, or copying of this email is strictly prohibited. = =3D If you have received=3D20 this email in error please notify the sender immediately. Please note = =3D that we reserve=3D20 the right to monitor and read any emails sent and received by the =3D Company in=3D20 accordance with and to the extent permitted by applicable legal rules. *************************************************************************= =3D **************************** =3D20 =3D20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =3D20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin to unsubscribe: =3D mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave =3D20 =20 =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin to unsubscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave =20 *************************************************************************= **************************** This email and any files transmitted with it are confidential and = intended solely for the=20 use of the individual or entity to whom they are addressed. If you are = not the intended=20 recipient or the person responsible for delivering the email to the = intended recipient, be=20 advised that you have received this email in error that any use, = dissemination,=20 forwarding, printing, or copying of this email is strictly prohibited. = If you have received=20 this email in error please notify the sender immediately. Please note = that we reserve=20 the right to monitor and read any emails sent and received by the = Company in=20 accordance with and to the extent permitted by applicable legal rules. *************************************************************************= **************************** =20 =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin to unsubscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave