The Inhibited Alarms Report never ran reliably at our site, we also discovered 
this by chance back in Dec 2010 and we raised a CAR for it but never got to the 
end of it.
In our case, the faceplate of the block did not show the "inhibited sign" even 
though the button was marked as "enable" indicating that it is indeed 
inhibited. The report did not capture it. Moreover, the ALMSTA parameter did 
not change whether the alarm was inhibited or not. 
We suspected, but did not confirm, that this happened when the enabled alarming 
options were only the BAD/OOR combinations.

Regards,
Assem Abdou
PS : Unless you really need to, please don't print this email

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On ;
Behalf Of Tadeo Armenta
Sent: Monday, April 10, 2017 11:25 PM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] FoxSelect "Blocks with inhibited alarms" report not 
updating

Silly questions first...

Are you sure all the stations are connected for the update (ie. they are blue 
on foxselect)??

Regards

--------------------------------------------
El mar, 4/11/17, Currano, Joe <Joseph.Currano@xxxxxxx> escribió:

 Asunto: [foxboro] FoxSelect "Blocks with inhibited alarms" report not updating
 A: "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>
 Fecha: martes, 11 de abril de 2017, 09:11 am
 
 Has anyone had a problem with FoxSelect  reports not updating even though you 
click Refresh? I have  configured a report to show "Blocks with Inhibited 
Alarms"
 selecting all CPs and all alarm types, all Compounds and  Blocks. I created 
this in December on one operator  workstation so they could look at and print a 
list of  inhibited alarms from there. Seemed to work fine that day,  never 
checked back until today. Now I see that when I click  Refresh, even though it 
looks like it refreshes, it doesn't  actually add the newly inhibited alarms to 
the list (spot  checked a couple that are now inhibited). Seems to be stuck  on 
the data it got long ago. Besides the regular Refresh  menu option and button 
in the Report View, I tried Refresh  All from the Station View, even tried 
configuring a whole  new report and it didn't get the new ones either.
 I think we're on FoxView 10.4 on this
 workstation, IA v9.x, on the Mesh. We have a mix of stations  on the Mesh and 
on the Nodebus, but it seems like it's not  updating inhibited blocks from any 
station, whether on Mesh  or Nodebus side.
 
 Just wondering if anyone has seen this
 and knows a fix/workaround. We have System Auditor but want  to have 
flexibility to use FoxSelect reports also,  especially since SA only updates 
once a day and this one  should be real time.
 
 -Joe
 
  
  
 _________________________________________________________________________
 This mailing list is neither sponsored
 nor endorsed by Schneider Electric
 (formerly The Foxboro Company).
 Use the info you obtain here at your own  risks.  See the disclaimer at  
www.thecassandraproject.org/disclaimer.html
  
 foxboro mailing list:
            //www.freelists.org/list/foxboro
 to subscribe:
      mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
 to unsubscribe:
   mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
  
 
 
 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric 
(formerly The Foxboro Company).  Use the info you obtain here at your own 
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_________________________________________________________________________
This mailing list is neither sponsored nor endorsed by Schneider Electric
(formerly The Foxboro Company).  Use the info you obtain here at your own
risks.  See the disclaimer at www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:               //www.freelists.org/list/foxboro
to subscribe:           mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:        mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: