Re: [foxboro] FBM231 modbus with siemens

  • From: Corey R Clingo <corey.clingo@xxxxxxxx>
  • To: foxboro@xxxxxxxxxxxxx
  • Date: Mon, 22 Oct 2007 17:26:55 -0500

Is there a block configured to read address 40001 in this application?

If not, this certainly sounds like an overreaction on the part of the 
Siemens PLC, but the FBM231 is not completely blameless; it should not be 
polling for unconfigured data.


Corey Clingo
BASF Corporation






"Wilson, Brad" <brad.wilson@xxxxxxxxxxxxxxxx> 
Sent by: foxboro-bounce@xxxxxxxxxxxxx
10/19/2007 09:03 AM
Please respond to
foxboro@xxxxxxxxxxxxx


To
<foxboro@xxxxxxxxxxxxx>
cc

Subject
Re: [foxboro] FBM231 modbus with siemens





In trying to set up a FBM231 with a Siemens S7, I discovered that the
FBM231 tries to establish a comm link with the PLC before sending a
request. In the absence of a heartbeat, it sends a read request to
address 40001 (the first entry of the holding register. If the Siemsns
receives a request to an undefined address, it shuts down the comm port.
So, if 40001 is undefined then the PLC immediately goes off-line and can
only be restored by cycling power. There may be other "odd" behaviour
associated with Siemens too. Be sure that heartbeat (FC8) is turned on.
It would seem that standard modbus is not always so "standard".

Brad Wilson
brad.wilson@xxxxxxxxxxxxxxxx
Invensys Systems, Inc
1090 King Georges Post Rd, Suite 204
Edison, NJ  08837
732-874-0087




 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: