Is there a block configured to read address 40001 in this application? If not, this certainly sounds like an overreaction on the part of the Siemens PLC, but the FBM231 is not completely blameless; it should not be polling for unconfigured data. Corey Clingo BASF Corporation "Wilson, Brad" <brad.wilson@xxxxxxxxxxxxxxxx> Sent by: foxboro-bounce@xxxxxxxxxxxxx 10/19/2007 09:03 AM Please respond to foxboro@xxxxxxxxxxxxx To <foxboro@xxxxxxxxxxxxx> cc Subject Re: [foxboro] FBM231 modbus with siemens In trying to set up a FBM231 with a Siemens S7, I discovered that the FBM231 tries to establish a comm link with the PLC before sending a request. In the absence of a heartbeat, it sends a read request to address 40001 (the first entry of the holding register. If the Siemsns receives a request to an undefined address, it shuts down the comm port. So, if 40001 is undefined then the PLC immediately goes off-line and can only be restored by cycling power. There may be other "odd" behaviour associated with Siemens too. Be sure that heartbeat (FC8) is turned on. It would seem that standard modbus is not always so "standard". Brad Wilson brad.wilson@xxxxxxxxxxxxxxxx Invensys Systems, Inc 1090 King Georges Post Rd, Suite 204 Edison, NJ 08837 732-874-0087 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave