[SI-LIST] Re: Is Impedance Enough for Describing the PDS?

  • From: Larry Smith <Larry.Smith@xxxxxxx>
  • To: "si-list@xxxxxxxxxxxxx" <si-list@xxxxxxxxxxxxx>
  • Date: Fri, 16 Jul 2004 10:40:44 -0700

Scott and Steve have both had some good comments on the importance of
mounting inductance for decoupling capacitors.  The mounting
inductance is almost inversely proportional to the number of vias used
to attach the capacitor to the power planes and proportional to the
length of the vias (depth to the first plane).  The number of high
frequency capacitors required to meet a PDS target impedance is nearly
proportional to the mounting inductance over the frequency range that
we care the most about.  So in a sense, the number of vias is
important, the number of capacitors is not.  

Ten years ago, the typical mounting inductance for decaps was 3 to 5
nH as we used traces to vias; to power planes; that were buried in the
middle of our boards; usually with 14 mils or more separation between
planes.  We sometimes shared vias between 2 or more caps!  As
mentioned by Scott, it is now possible to attach capacitors with a
total mounting inductance of 200pH or less.  So the number of
capacitors necessary to meet a target impedance a decade ago was 20
times more than what it is today.  Actually, the number of capacitors
has stayed about the same and the target impedance has dropped by
about a factor of 20.

When you think about it, all we really need is a single ideal 1 uF
capacitor connected to our PDS.  The impedance of a 1 uF capacitor at
1 MHz is 159 mOhms.  It is 15.9 mOhms at 10 MHz, 1.59 mOhms at 100 MHz
and 0.159 mOhms at 1 GHz.  Imagine that, a PDS with much less than 1
mOhm at a GHz!  And all you need is one ideal capacitor!  The moral of
this story is that a low impedance PDS at high frequency has very
little to do with capacitance and is all about managing the parasitic
inductance.

Small power islands work great for core power.  Just put enough
capacitors (and vias) in parallel that you achieve the target
impedance up to the desired corner frequency.  It does not take too
many well-mounted capacitors in parallel to do this.  The biggest
problem is that the impedance of the parallel combination of all caps
mounted on the plane becomes less than the impedance of the power
planes used to bring the current into the chip.  This is where the
thin power plane dielectric (BC) comes in.  Once again, it is not
about capacitance but is all about spreading inductance.  If the
impedance of the conduit is higher than that of the parallel caps,
don't bother putting any more caps on the board..

The subject of this thread is, "Is Impedance Enough for Describing the
PDS?"  For the purpose of power integrity (getting the power to the
consumer when it is required and stop delivering power to the consumer
when it is not required), the answer is a resounding YES!  If the chip
circuits look out and see their target impedance up to a frequency
that is related to the transient rise time, they are happy.  If the
chips are happy, they don't make EMI noise.  EMI noise is just a
result of chips demanding current from a PDS that is too high in
impedance.  Current drawn from a high impedance implies power injected
into the PDS and that is trouble.  Manage the PDS impedance at the
power consumer and (PDS related) EMI problems will be greatly reduced
or go away completely.

regards,
Larry Smith
(still at) Sun Microsystems

PS - Boy, I sure miss Ray!

steve weir wrote:
> 
> Zhangkun,
> 
> As I stated, the mounted inductance of IDC's and X2Y's is less than 1/3 the
> mounted inductance of ordinary 0603's using optimized two via mounts.  The
> inductance of the IDC / X2Y capacitors by themselves is even less, but as
> you note the attachment inductance interferes.  The reason that IDCs do
> very well is that it takes four times as many via holes as a regular
> capacitor.  Done correctly, there is an almost proportionate decrease in
> the attachment inductance.  So, an IDC can be viewed as four 0603s, in
> parallel but with only one part to mount.
> 
> The physics of the X2Y are a bit different.  In cooperation with X2Y, I
> have developed optimized mounts for X2Ys that use six vias and get results
> essentially identical to the IDC with optimal mounts.  This has been
> verified by both simulation and measured results.  The IDC's require 33%
> more vias, and a much higher component cost to do the same decoupling job
> as X2Ys.
> 
> Using either X2Y or IDCs we can cut component count by 3:1 or
> better.  Using X2Ys we reduce the BOM cost as well.  Both Teraspeed and I
> offer services to optimize PDS design to suite needs whether it is density,
> cost or some combination.  There are probably other consultants available
> who do as well.
> 
> Regards,
> 

Scott McMorrow wrote:
> 
> Zhangkun,
> 
> Zhangkun wrote:
> 
> >How about the value of the inductance of these kind of capacitors? When the 
> >cap is soldered on the PCB, there is leading inductance of about 1nH. This 
> >could not be eliminated by better caps.
> >
> Actually, better designed capacitors and better mounting structures do
> help.  Steve and I both have developed mounting structures for some of
> these capacitors that are down in the 200 pH range, with a total mounted
> device inductance below 400 pH.  It's all a matter of physics and good
> design practices.  With X2Y and IDC capacitors, we can obtain between a
> 3 and 4-to-1 part count reduction over 0603 capacitors with the best
> designed mounting solution.
> 
> regards,
> 
> scott
> 
> --
> Scott McMorrow
> Teraspeed Consulting Group LLC
> 121 North River Drive
> Narragansett, RI 02882
> (401) 284-1827 Business
> (401) 284-1840 Fax
> (503) 750-6481 Cellular
> http://www.teraspeed.com
> 
> Teraspeed is the registered service mark of
> Teraspeed Consulting Group LLC
>
------------------------------------------------------------------
To unsubscribe from si-list:
si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field

or to administer your membership from a web page, go to:
//www.freelists.org/webpage/si-list

For help:
si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field

List FAQ wiki page is located at:
                http://si-list.org/wiki/wiki.pl?Si-List_FAQ