Jack, thanks. I will have to go back and look, but in the old days of 1950 we got a pass on the telecom equipment for SELV, and then with 1950A, my understanding has been that the pass was revoked. I have carried that impression around for the decade or so since 1950A came and went over a decade ago. Now I will have to see if I have been laboring under a misconception for a decade. Regards, Steve. At 01:30 PM 10/19/2004 -0400, Murphy Jack-MGI2488 wrote: >Steve, > >The low voltage safety limit is actually >60Vdc or >42.4Vpeak. Under >those limits the circuit is considered SELV and spacings do not >apply. For centralized DC power inputs, UL requires a 500Vac (707Vdc) >hipot test between 48Vdc/RET and chassis to verify isolation. We make >CO-type equipment powered via a -48Vdc centralized DC power source and we >use UL60950-1 for Product Safety. > >A 48Vdc battery power system has a float up to 60Vdc which is still under >the SELV limit. > >The National Electric Code has DC power source limitations (voltage vs >current) that they classify Class 2 or 3. I'll admit that I'm not very >familiar with the NEC. > >Jack Murphy >SR Compliance Engineer >Motorola BCS > >-----Original Message----- >From: si-list-bounce@xxxxxxxxxxxxx [mailto:si-list-bounce@xxxxxxxxxxxxx] >On Behalf Of steve weir >Sent: Tuesday, October 19, 2004 1:06 PM >To: tcuratolo@xxxxxxxx; si-list@xxxxxxxxxxxxx >Subject: [SI-LIST] Re: 48V power distribution > > >Tom, the biggest issue is that 48V exceeds the 42V low-voltage safety limit >and so requires substantially greater clearances. A 24V system is under >that limit and does not face the same problem. 48V also changes the >dynamics of available semiconductors. 12V systems and to a certain extent, >24V systems can leverage the super low on resistance and low capacitance >FETs and diodes. The last issue is one of magnetics and practical >form-factors. Given you work for Vicor, you should be pretty familiar with >those and how taller primary to output ratios aggravate same. > >Regards, > > >Steve >At 02:04 PM 10/19/2004 +0000, tompegbel wrote: > > >Is there a good resource/document for addressing the concerns in > >bussing 48V power in a multilayer board? The recently popular 12V or > >lower intermediate bus approach has limitations as voltages get lower > >and current gets higher. There appears to be new approaches of using a > >higher bus voltage (24V or 48V) for distribution since this was > >explored in the 80's with the advent of distributed power and now more > >recently with VoIP type designs. Any assistance appreciated > > > > > > > >------------------------------------------------------------------ > >To unsubscribe from si-list: > >si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field > > > >or to administer your membership from a web page, go to: > >//www.freelists.org/webpage/si-list > > > >For help: > >si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field > > > >List FAQ wiki page is located at: > > http://si-list.org/wiki/wiki.pl?Si-List_FAQ > > > >List technical documents are available at: > > http://www.si-list.org > > > >List archives are viewable at: > > //www.freelists.org/archives/si-list > >or at our remote archives: > > http://groups.yahoo.com/group/si-list/messages > >Old (prior to June 6, 2001) list archives are viewable at: > > http://www.qsl.net/wb6tpu > > > > >------------------------------------------------------------------ >To unsubscribe from si-list: >si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field > >or to administer your membership from a web page, go to: >//www.freelists.org/webpage/si-list > >For help: >si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field > >List FAQ wiki page is located at: > http://si-list.org/wiki/wiki.pl?Si-List_FAQ > >List technical documents are available at: > http://www.si-list.org > >List archives are viewable at: > //www.freelists.org/archives/si-list >or at our remote archives: > http://groups.yahoo.com/group/si-list/messages >Old (prior to June 6, 2001) list archives are viewable at: > http://www.qsl.net/wb6tpu > ------------------------------------------------------------------ To unsubscribe from si-list: si-list-request@xxxxxxxxxxxxx with 'unsubscribe' in the Subject field or to administer your membership from a web page, go to: //www.freelists.org/webpage/si-list For help: si-list-request@xxxxxxxxxxxxx with 'help' in the Subject field List FAQ wiki page is located at: http://si-list.org/wiki/wiki.pl?Si-List_FAQ List technical documents are available at: http://www.si-list.org List archives are viewable at: //www.freelists.org/archives/si-list or at our remote archives: http://groups.yahoo.com/group/si-list/messages Old (prior to June 6, 2001) list archives are viewable at: http://www.qsl.net/wb6tpu