Thanks guys, I'll set up a couple of different approaches (didn't try
the dtime/calc combination yet, so I'll give that a try) and see which
are most accurate.
Thanks for the suggestions,
Rgds,
Dirk
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Jerry Hidahl
Sent: vrijdag 14 juli 2006 16:59
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] flowrate
Dirk,
It seems you want to calculate a flow rate from the rate of change of
the
bin weight. I did something similar in order to calculate a rate of
change
for a pressure measurement, by using a dead-time (DTIME) block and a
calc
block. The dead-time block is on a 1 second period and delays the
reading
exactly six seconds (0.1 minutes). The calc block subtracts the current
value from the delayed value and divides by the dead time to get the
rate
(or actually multiplies by ten). This arrangement gives readings updated
every second, but they are a bit noisy, due to the additive effect of
the
error of the actual measurement. If you use a longer dead time you can
reduce the effect of measurement error on the rate calculated, but it
will
be at the expense of frequent updates. You just have to find the best
compromise for your application. You can do better than calculating the
rate once per minute.
The dead-time block uses up to ten discrete "buckets" to hold the old
value. I used six buckets. By default, the algorithm averages the input
values and interpolates the delayed values to give a more continuous
measurement with the limited number of buckets. There's an option
(DTOPT)
to disable averaging and interpolation so that only actual values are
stored and indicated. I chose to use actual values.
Once the rate of change is calculated, it can be connected to an AIN
block
for filtering and alarming.
Jerry Hidahl
Huntsman Performance Products
=20
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
=20
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: