Look at document B0400FK, section 5. Table 5-5 (page 44) shows that you
can swap bytes, even across words. Hopefully this helps. I'm not familiar
with FRIN blocks.
Steve Shimp
Maintenance & Systems Engineer
ExxonMobil Paulsboro Lube Plant
phone: 856.224.5059 cell: 609.820.8501 fax: 856.224.5030
email: steve.shimp@xxxxxxxxxxxxxx
foxboro-bounce@xxxxxxxxxxxxx wrote on 02/14/2006 08:52:34 AM:
> Steve,
>
> thanks, but my Real value is 32-bit IEEE-754 Floating Point format, lik=
> e
> this:
>
>
>
> Decimal Value Entered: 12.34
>
>
> Single precision (32 bits):
>
>
> Binary:=A0=A0=A0=A0=A0Status: normal
> |-------------+--------------------------------------------------------=
> --+------------------------------------------------|
> | | =
> | |
> | Bit 31 | =
> | |
> | Sign Bit | Bits 30 - 23 =
> | Bits 22 - 0 |
> | 0 | Exponent Field =
> | Significand |
> | 0: + | 10000010 =
> | 1 .10001010111000010100100 |
> | 1: - | Decimal value of exponent field and exponent =
> | Decimal value of the significand |
> | | 130 - 127 =3D 3 =
> | 1.5425000 |
> | | =
> | |
> | | =
> | |
> |-------------+--------------------------------------------------------=
> --+------------------------------------------------|
>
>
>
>
> Hexadecimal: 414570A4=A0=A0Decimal: 12.340000
>
>
>
> The FRIN Block read it in the right way, if the Modbus-Words are in the=
>
> right order. But it isn't in my case.
>
> Regards
>
> Rolf Reber
> ____________________________________
> EMS-CHEMIE AG
> Business Unit EMS-SERVICES
> Abt. Anlagenbau / Prozessleitsysteme
> Reichenauerstrasse
> CH-7013 Domat/Ems
>
> Phone: +41 (0) 81 / 632 71 49
> Fax: +41 (0) 81 / 632 74 04
> mailto: rolf.reber@xxxxxxxxxxxxxx
> http://www.emsservices.ch
>
>
> |---------+---------------------------->
> | | steve.shimp@exxon|
> | | mobil.com |
> | | Sent by: |
> | | foxboro-bounce@fr|
> | | eelists.org |
> | | |
> | | |
> | | 14.02.2006 14:21 |
> | | Please respond to|
> | | foxboro |
> | | |
> |---------+---------------------------->
> >--------------------------------------------------------------------=
> -----------------------------------------------------------------------=
> -------|
> | =
> =
> |
> | To: foxboro@xxxxxxxxxxxxx =
> =
> |
> | cc: =
> =
> |
> | bcc: =
> =
> |
> | Subject: Re: [foxboro] Word-Swaping on Modbus Interface Micr=
> o I/A =
> |
> >--------------------------------------------------------------------=
> -----------------------------------------------------------------------=
> -------|
>
>
>
>
> Rolf,
>
> We have done this with RIN blocks on a Modbus interface. The "trick" i=
> s to
> use 2 separate RIN blocks for each 16-bit word. Then use a CALC block =
> to
> manipulate the two values from the RIN blocks to determine the original=
>
> value.
>
> For example, there is a value transmitted over the Modbus interface tha=
> t is
> 67098.2 originally. The words are transmitted such that the first word=
> is
> the low order bits and the second word is the high order bits. The fir=
> st
> word is pulled into a RIN block that has an MGAIN value of 0 (zero). T=
> he
> second word is pulled into a RIN block that has a MGAIN value of 1000
> (based upon the documentation of the Modbus sending device and how the
> interface is designed). The RIN blocks are therefore "reading" 98.2 fo=
> r
> the low order and 67000 for the high order. Pull these RIN blocks into=
> a
> CALC block and simply add them together.
>
> Hope this helps.
>
>
> Steve Shimp
> Maintenance & Systems Engineer
> ExxonMobil Paulsboro Lube Plant
> phone: 856.224.5059 cell: 609.820.8501 fax: 856.224.5030
> email: steve.shimp@xxxxxxxxxxxxxx
>
> foxboro-bounce@xxxxxxxxxxxxx wrote on 02/14/2006 08:00:55 AM:
>
> >
> > Hi List,
> >
> > our I/A-System is Unix V6.4 and Micro I/A V6.2.5 with 2 Modbus serial=
>
> > Interfaces attached. I would like to read/write data from/to a Modbus=
>
> > Device (Brabender weighing unit) with FRIN /FROUT blocks. But the two=
>
> 16bit
> > Modbus Words for a real value are in wrong order. Example: Value 12.=
> 34
> in
> > the Modbus Adresses 47200 and 47201 (Value Hex 70A4 4145) will be
> displayed
> > on FoxView as 4017238209...................... How can I change the O=
> rder
> > of the Modbus Adresses to 47201 and 407200 (Value Hex 4145 70A4) on t=
> he
> > I/A-System? There is no way to change it on the Modbus Device!
> >
> > Thanks for helping,
> >
> > Regards
> >
> > Rolf Reber
> > ____________________________________
> > EMS-CHEMIE AG
> > Business Unit EMS-SERVICES
> > Abt. Anlagenbau / Prozessleitsysteme
> > Reichenauerstrasse
> > CH-7013 Domat/Ems
> >
> > Phone: +41 (0) 81 / 632 71 49
> > Fax: +41 (0) 81 / 632 74 04
> > mailto: rolf.reber@xxxxxxxxxxxxxx
> > http://www.emsservices.ch
>
>
>
> _______________________________________________________________________=
>
> This mailing list is neither sponsored nor endorsed by Invensys Process=
>
> Systems (formerly The Foxboro Company). Use the info you obtain here at=
>
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html=
>
>
> foxboro mailing list: http://www.freelists.org/list/foxboro=
>
> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djo=
> in
> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dlea=
> ve
>
>
> =
>
>
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list: http://www.freelists.org/list/foxboro
> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: