        The Foxboro documentation that answers your questions is:
Network Cable Systems Installation and Maintenance      B0193UW, Rev D
Network Cable Systems Planning                          B0193UX, Rev E
I/A Series A2 Nodebus/Control Network Interface(NCNI)   PSS 21H-7B5 B4

        The maximum fiber optic fieldbus Cable Length is 4 km (point to point). 
 If
it were my installation I would lean toward the Fiber Optic Fieldbus based
on past problems with nodebus extenders, but the fiber optic capabilities of
the NCNI's may provide a good solution.  However, Foxboro documentation,
(PSS 21H-7B5 B4), has a stated point to point distance limitation of 2km and
it sounds like you may be pushing that.

There are a few considerations to think about:
Can you forsee a need to install nodebus equipment in the remote location in
the future?
It is always wise to pull additional fibers.  You will need 4 fibers if you
want a dual nodebus or fieldbus so you would probably install a 6 fiber
cable anyway.  But compared to the cost of installing 6 fibers, installing
12 isn't much more expensive and it would give you the future capability to
have both nodebus and fieldbus communication at the remote location.

Tom VandeWater
Control Systems Developer/Analyst
Dow Corning Corporation
Carrollton, KY  USA

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx
[mailto:foxboro-bounce@xxxxxxxxxxxxx]On Behalf Of Ajay.Tathgir@xxxxxxx
Sent: Saturday, January 31, 2004 1:22 AM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Optical Field Bus / NCNI's

Hi! All

Wanted to know how long can i run a field bus using the optical cable. The
issue is that the present system is at location 0, and there is another
unit around 1.5 kms away. I was thinking of putting the CP's at location 0
& using a optical field bus to connect to FBI's around 1.5 kms away. The
1.5 could be 2.5 also.

Or should i create a extended node and connect the same using NCNI's
through a optical link. In the present system i've four 1 X 8 MS, and i'll
have to add two 1 X 8 MS at the new location.

It would be good to know if there are issues involved with any of the above
configurations.

The system is 6.1.2 Unix having 51B stations.


TIA & Regards


Ajay Tathgir

Reliance Industries Limited
Mumbai - India



_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html

foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave


 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: