Re: [foxboro] Node Troubles????

Dale,

If there does not seem to be a sign of a reboot, then it is not likely
that the extender is causing this problem, unless there are peer
connections into these blocks with some specific logic to force to
Manual given OOS, or BAD, etc.

So if you don't have peer or specific logic, then I would look at=20

1. Sequence blocks using some infrequently used logic. If you have
sequence logic I would put all the .s files in a directory and search
for the .MA of some of your blocks.

2. Displays, again some infrequently called display that might have some
DM commands imbedded (somebody builds a test display and forgets to
delete it) that toggle the.MA parameters of some blocks.  Here I would
"strings" through the display files and "grep" for the .MA of your
blocks.  You can easily build a script to check all files in a directory
and output the name of the displays that have .MA imbedded.

3. Is there any off-node access via AIMAPI or FoxAPI where someone might
have a spreadsheet (for example) that can "poke" your blocks .MA
parameter?

Your problem seems to be a very specific action and if you can rule out
initialization it seems impossible that a random event generating noise
can toggle this specific action.

Terry
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             http://www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: