Re: [foxboro] Modbus Slave
- From: Kevin FitzGerrell <fitzgerrell@xxxxxxxxxxxxxxx>
- To: foxboro@xxxxxxxxxxxxx
- Date: Thu, 15 Dec 2005 07:40:19 +1300
Joe,
One way to do this is to use a Modbus slave device in between the two
masters. ProSoft modules are a convenient device to use for this as
they can be configured with a number of Modbus slave ports.
Regards,
Kevin Fitzgerrell
Carter Holt Harvey, Ltd.
+64 27 460 9994
Joe Gale (MP) wrote:
> I was wondering if there is a way to make a Modbus connection to Foxboro
> where Foxboro is the slave device? Reading through the FBM224
> documentation, it says that the gateway has to be the master. We want
> to be able to talk to a GE Harris D20 RTU and I am being told that they
> will only do it with the RTU as master. Anyone have a viable solution?
> Thanks,
>
> Joe Gale
> DCS Administrator
> Minnesota Power
> 1210 NW 3rd Street
> Cohasset, MN 55721
>
> 218-328-5036 x4611
> email:jgale@xxxxxxxxxxx
>
>
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list: http://www.freelists.org/list/foxboro
> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>
>
>
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- References:
- [foxboro] Modbus Slave
- From: Joe Gale (MP)
Other related posts:
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- » Re: [foxboro] Modbus Slave
- [foxboro] Modbus Slave
- From: Joe Gale (MP)