Re: [foxboro] Modbus Communications between FBM224 and Trident SIS
- From: Gregory A Hurwitt <gregory.hurwitt@xxxxxxxx>
- To: foxboro@xxxxxxxxxxxxx
- Date: Thu, 28 Jun 2007 15:47:45 -0500
Arrange your boolean data that is to be transmitted to the I/A in
contiguous blocks of boolean memory in the Trident. (This is fairly
standard practice for communicating data from PLC's to DCS's.) The latest
version (V4) of Tristation software gives you plenty of flexibility in
assigning the Modbus aliases to do this.
Once you've done this you should have no problem using PAKIN blocks to
bring across 32 bits at a time. The use of CIN's downstream is optional,
depending on what you're doing with the data. If you want alarms, you'll
need CIN (or BLNALM) blocks. If you're just connecting to displays or to
control logic, you could connect directly to the PAKIN's. However, using
CIN's in all cases in order to assign a tag name to each signal is
generally beneficial.
______________________________________________________________________________________
Greg Hurwitt
Engineering Associate
E-Mail: gregory.hurwitt@xxxxxxxx
Postal Address:
BASF Corporation
602 Copper Road
Freeport, TX 77541
USA
BASF - The Chemical Company
"Dennis
Stone"
<DStone@ To
HUNTREFI <foxboro@xxxxxxxxxxxxx>
NING.com cc
>
Sent by: Subject
foxboro- [foxboro] Modbus Communications
bounce@f between FBM224 and Trident SIS
reelists
.org
06/28/20
07 02:25
PM
Please
respond
to
foxboro@
freelist
s.org
Afternoon,
We recently installed and commissioned our first and second SIS
(Trident) system at our refinery. The engineering/integration firm
hired for the project implemented communications between the I/A and the
Trident using MODBUS and 100's of IIN blocks tied to CIN's for display
and alarming. My question is whether anyone has implemented MODBUS to a
Trident using a PAKIN block and then linking to CIN's for diplay and
alarming. Our current setup puts a tremendous load on our CP because
each status (single bit) is being represented/transmitted as an integer
value, causing overruns every 15 seconds. I tried a test using a 32 bit
packed interger value from the trident and bringing that into a PAKIN
block but it doesn't appear that the PAKIN can decode the integer into a
32 binary word. Any suggestions???
Any feedback is greatly appreciated.
Dennis Stone
Process Control Engineer
Hunt Refining Company
dstone@xxxxxxxxxxxxxxxx <mailto:dstone@xxxxxxxxxxxxxxxx>
(205) 391-3303
(205) 391-3564 FAX
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- References:
- [foxboro] Modbus Communications between FBM224 and Trident SIS
- From: Dennis Stone
Other related posts:
- » Re: [foxboro] Modbus Communications between FBM224 and Trident SIS
- » Re: [foxboro] Modbus Communications between FBM224 and Trident SIS
- [foxboro] Modbus Communications between FBM224 and Trident SIS
- From: Dennis Stone