Although it doesn't use the iccprt output, it might be worth looking at=
Foxboro's HH1068.
I've included the text below.
Kevin FitzGerrell
Systems Engineer
Foxboro New Zealand
------------------------------------
Tel: +64 (9) 573 7690
Fax: +64 (9) 573 7691
HH#: HH1068
IA INFO: sja0403
File: Control, Alarm=
s
Release: All
Date: Nov 04, 2004
Subject: Determining Which Alarms Are Configured On Your System, Per B=
lock
Source: TAC
Here is a procedure that uses the utility program "getpars" to determin=
e
the alarm types that are set on your system for each of the blocks.
"getpars" is very flexible and has several options. Look at the
getpars.man file (in /opt/fox/bin/tools) to see the complete list of
options. The following is just one example.
Log into your system in VT100 and go to the tools directory.
cd /opt/fox/bin/tools
Run the following command:
getpars ?U\* -C\* -B\* -mCMPNM:%12s ?mTYPE:%6s ?mALMOPT:%8x >
alarm.txt
The command options are as follows:
-U\* all cp's
-C\* all compounds
-B\* all blocks
-mCMPMN:%12s prints the compound name as a 12-character stri=
ng
-mTYPE:%6s prints the type of block as a 6-characters stri=
ng
-mALMOPT:%8x prints the parameter ALMOPT as an 8-digit hex
number
> alarm.txt redirects the output to a file called alarm.txt=
The backslashes are required before the asterisks so that the Unix shel=
l
will not evaluate the * as filenames.
Here is an example of the output:
COMPOUND-NAME AC_PIDA (CP-LETTERBUG: CP660F)
BLOCK-NAME CMPNM TYPE ALMOPT
CALC AC_PIDA CALC NA
AIN1 AC_PIDA AIN 0
AIN AC_PIDA AIN 13430080
PIDA AC_PIDA PIDA 0
FBTUNE AC_PIDA FBTUNE NA
AOUT AC_PIDA AOUT 0
LLAG AC_PIDA LLAG NA
DTIME AC_PIDA DTIME NA
DEP AC_PIDA DEP 0
In this example only AC_PIDA:AIN has alarm options set.
When the value shows "NA", it means that that parameter does not apply =
to
that block type.
To determine what is set for this block convert the hex number into bin=
ary.
1 3 4 3 0 0 8 0 (Hex)
0001 0011 0100 0011 0000 0000 1000 0000 (Bin)
Then look up the ALMOPT parameter in B0193AX, Control Block Description=
s.
Here is the ALMOPT parameter for an AIN block.
B4=3D Out-of-Range Alarm, B7=3DHHALM, B8=3DLLALM, B15=3DHABS, B16=3DLAB=
S, B7=3DAlarm
Group 1
This is for an AIN. All the other blocks are listed in the document an=
d,
if they have an ALMOPT, parameter, the individual option bits will be
shown.
A general description of the parameter for all block types is given as =
a
table in B0193AW, Integrated Control Concepts.
HH1068
=
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- Follow-Ups:
- Re: [foxboro] Listing all Configured Alarms
- From: Kevin FitzGerrell
Other related posts:
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- » Re: [foxboro] Listing all Configured Alarms
- Re: [foxboro] Listing all Configured Alarms
- From: Kevin FitzGerrell