To add to this, after some further thought, and respond to your comment:

"It all goes back to the basic design assumption - A WP hosts FoxView and 
FoxAlert instances that are closely coupled. If you need alarm 
segregation, the assumption is that you'll buy separate WPs."


FoxAlert == Alarm MAnager?


I can go along with this for the horns. Horns are inherently WP-global 
entities anyway.


However, you have one AM and one FV/DM that are linked. You invoke 
filtering on the AM. That filtering only affects that AM instance, 
correct? If so, there's no reason that the Alarms/Process button on the 
linked FV/DM shouldn't be subject to the filter as well.


My comment in my last response (below) about telling the operator to 
ignore the flashing bar that message events cause is not really correct. 
The DM/FV linked to my "message" AM will probably not matter, as it would 
be hidden/minimized most likely, but the  primary DM/FV's button will also 
flash. So it will still be a problem, at the least from a confusion 
standpoint.


Corey Clingo



From:   Corey R Clingo <corey.clingo@xxxxxxxx>
To:     foxboro@xxxxxxxxxxxxx
Date:   05/10/2012 03:05 PM
Subject:        Re: [foxboro] Installing IA series V8.X on Zone 2 
workstation
Sent by:        foxboro-bounce@xxxxxxxxxxxxx



I'll give you a couple of reasons:

First, the original topic was thin clients. The use case for these is 
being able to host more than one from a single server. Ideally, you'd have 

a few servers that a given thin client could pull a display from, for 
redundancy. If I don't have all the servers set up identically as alarm 
destinations, then I can't really do that, as the AMs on the different 
servers behave differently. This effectively makes my required number of 
servers be 2 * N minimum, rather than just 2 or 3, where N is the number 
of different plant areas or whatever I have that would require different 
alarm destination configuration.


Second, and this is a problem we face now, I would like to have one or two 

"extra" AMs for operator messages. I was planning originally to use CAD 
filtering for that, but I will have the flashing-Alarms-button problem. It 

doesn't make much sense in my mind to buy, house, and maintain an entire 
WP for one AM screen. As it stands, I'm just going to have to tell the 
operators to ignore the flashing bar on that screen.


I realize that at one time the assumption you refer to was valid. But I 
think in our new world of rationalized alarms (and "new-old" world of thin 

clients) we might do well to  revisit that assumption.


Corey Clingo



From:   "Johnson, Alex P (IOM)" <Alex.Johnson@xxxxxxxxxxxx>
To:     "foxboro@xxxxxxxxxxxxx" <foxboro@xxxxxxxxxxxxx>
Date:   05/10/2012 02:29 PM
Subject:        Re: [foxboro] Installing IA series V8.X on Zone 2 
workstation
Sent by:        foxboro-bounce@xxxxxxxxxxxxx



There is an assumption that the "slave" FV displays share a common plant 
area and, therefore, receive the same alarm set.

As I understand what you are telling me, you have different "plant areas" 
using FoxView/FoxAlert from the same WP. If that's the case, you are using 

the software in a manner that contradicts our assumption.

Is this the case? If so, why not buy another WP?

Regards,
 
Alex Johnson
Invensys Operations Management
10900 Equity Drive
Houston, TX 77041
+1 713 329 8472 (desk)
+1 713 329 1600 (operator)
+1 713 329 1700 (Central Fax)
alex.johnson@xxxxxxxxxxxx 

 
 



 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: