On my similar application, I used a block exception handler with a dummy
wait in it. We are throwing the display up on multiple WPs so I didn't
bother retrying on the unresponsive WPs, but it does keep the IND block
from going to manual:
BLOCK_EXCEPTION TO_SYS_ERROR
STATEMENTS
{ Dummy code to make sequence continue at next WP if one
of them is offline }
WAIT 1.0;
ENDEXCEPTION
If you want to trap other kinds of exceptions, you may have to use more
intricate code, or this may not even work. But my application is simple,
and this was a perfect way to step over dead WPs.
Corey Clingo
BASF Corp.
Ron Schafer <rschafer@xxxxxxxxxxxxxxxxxxxxxx>
Sent by: foxboro-bounce@xxxxxxxxxxxxx
11/06/2009 12:45 PM
Please respond to
foxboro@xxxxxxxxxxxxx
To
"'foxboro@xxxxxxxxxxxxx'" <foxboro@xxxxxxxxxxxxx>
cc
Subject
[foxboro] IND Block error
Ok, I was surprised by a block error yesterday on a ind block (46IND5325).
Basically the code loops through a sequence of checks and events and
during one check it will send the following command IF a certain condition
exists.
:46AW03DMCMD := "dmcmd /OPT/MENUS/46AREA/PAPER_MACHINE/BROKE.FDF";
Normally the command will pull up a display (BROKE.FDF) on Foxview 46AW03.
Here is where the catch comes into play. The station(46AW03) had a
hardware problem and was not powered up or on the mesh and caused the seq
block to go to manual. Since the MA parameter is set to "MA =
:46IND5325.MA.1" The block would kick back into auto and fail again,
etc....
So my question to all is how would you handle the block so it doesn't fail
just because a workstation is not alive? Error handling routine? IF/Then
check? Some other means? I was very surprised that the block knew the
station was not reachable and the ind block went to manual!
Ronald G. Schafer
Distributed Controls System Administrator
White Birch Paper Company
Bear Island L.L.C. Division
10026 Old Ridge Road
Ashland VA, 23005
Phone 804-227-4034
Fax 804-227-4052
Email: rschafer@xxxxxxxxxxxxxxxxxxxxxx<
mailto:rschafer@xxxxxxxxxxxxxxxxxxxxxx>
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: