Re: [foxboro] I/A Batch Unix to I/A Batch Windows
- From: "Ghiglione, Alessandro" <Alessandro.Ghiglione@xxxxxxxxxxxx>
- To: <foxboro@xxxxxxxxxxxxx>
- Date: Thu, 9 Jul 2009 12:23:18 +0100
Dirk,
I forgot 2 aspects:
A) we move from one redundant BS (rel.8.0) to two separate BS for different
plant area.
It was possible as the 2 area are independent.
The redundancy in the past gave us more trouble than benefits!
Repeated master/backup switchover were intolerable.
B) in rel.8.0 we used the same value read delta=write delta=1.0
Now in rel.8.1 , actual values are 0.001 (read delta) and 0.49 (write delta).
When modifying a set point (write to CP) now the behaviour is consistent with
the delta value, while in rel.8.0 you read back the changed value even if below
the delta, as write delta were uninfluent....
BS EnvDisplay read/write delta values are written to FoxAPI.
I hope this help.
Alessandro Ghiglione
Senior Application Engineer
Infineum Italia s.r.l.
Strada di Scorrimento,2
17047 Vado Ligure (SV) - Italia
* +39.019.2150.277
mob. +39.3484535196
* +39.019.2150.326
* mailto:alessandro.ghiglione@xxxxxxxxxxxx
Infineum Italia S.r.l.
Cap. Soc. € 20.000.000,00 Int. Vers.
Sede legale: Via Lepetit 8 - 20124 Milano
Sede amm.va e stabilimento: Strada di Scorrimento 2 - 17047 Vado Ligure (SV)
Codice Fiscale e Partita IVA: IT12640380155
Reg. Imp. di Milano n. 255530/1998 - REA 1573108
Con Socio Unico
Informazione a norma dell'art. 2497-bis 1° c. CC: Infineum Netherlands B.V. -
Rotterdam (NL)
Questa nota può contenere informazioni ritenute confidenziali per Infineum. Se
è stata ricevuta non intenzionalmente: (a) si prega di non considerare le
informazioni contenute nella stessa; (b) non rivelare, distribuire o duplicare
alcuna informazione contenuta in questa nota; e (c) contattare l’autore.
This note may contain Infineum confidential information. If you are an
unintended recipient: (a) place no reliance on the information contained
herein; (b) do not disclose, distribute, or duplicate any information from this
note; and (c) please contact the author.
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of dirk.pauwels@xxxxxxxxxx
Sent: giovedì 9 luglio 2009 11.59
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] I/A Batch Unix to I/A Batch Windows
We're facing an upgrade from 8.0 on solaris to windows also, but not in
the near future.....
Regarding the conversion tool: our invensys contacts assured us there was
a tool available to convert the recipes, we have 400+ recipes so this is
an important issue. Could be the tool is officially released in the
meantime.
Right now we have some issues with the redundant version of BS 8.0 on
solaris, one AW51(E) is updating the transition values ok, the backup AW51
seems to use a delta of 1, which is not very useable if your transition
statements are waiting for pressure values in BAR....
Any one have an idea where these delta's are configured? It does not seem
to be in BS, Foxapi and backup BS settings for both stations are
identical.
Rgds,
Dirk
wrote:
David and all I/A Batch users,
Last february we migrated from rel.8.0 under Solaris to rel.8.1 under
Windows.
We prepared the migration in detail, with many checkpoints as we manage
>600 recipes, under a "large" IABatch licence.
Briefly, this is our experience:
1) ModelDB, IALinkDB and RecipeDB (still Raima based) need to be
converted.
A recipe conversion tool is not offered by Invensys (it is for internal
use only): so we paid the conversion as a consultant activity.
2) If you have developed some "C" programs based on Raima ToolKit, you
need to rewrite as new "COM" libraries are different, based on ActiveX. No
conversion is possible. Even with NutCracker.
3) Some tuning done on EnvDisplay parameters (and on FoxAPI too) due to
read/write tags timing issue.
Our case: when a recipe writes a tag (CP linked), you can read it updated
only after 1-2s; otherwise you must insert some "wait" transitions in the
recipe.
In december 2008 we moved from CP40(FT)/AW51E on nodebus to
CP270Z(FT)/P90/P92 on the Mesh, leaving IABatch on a Solaris AW51E
(Nodebus side with ATS): with this intermediate configuration, no
read/write problems occurred.
4)IALink: it was impossible to configure a bit >9 for a CP tag, now there
is a QF to solve it.
5)BatchDisplay: great flexibility now offered by zoomable SFC elements and
3 recipe layers on full sizeable windows!
Jump functionality is still available and working well, but it is less
flexible than before.
6)apart the usual care when you modify the code of a sequence in held
state (restart it after CP checkpoint is completed), I noted that
BatchManager crashed when operator started a new batch, where the first
phase/sequence in the recipe was changed and CP checkpoint not yet
finished.
Ugly, as it required a stop/restart of the whole Runtime tasks.
Luckily, hot restart feature works fine as in rel.8.0.
All the remaining features are kept: the feel & look is based on Windows,
but the speed is significantly better.
We don?t have yet a development platform to play with IABatch in more
detail; we played enough on the real platform in the second half of 2008,
when still off-line. There are some feature we don't use as we don't know
in deep...
Regards,
Alessandro Ghiglione
Senior Application Engineer
Infineum Italia s.r.l.
Strada di Scorrimento,2
17047 Vado Ligure (SV) - Italia
* +39.019.2150.277
mob. +39.3484535196
* +39.019.2150.326
* mailto:alessandro.ghiglione@xxxxxxxxxxxx
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: