To generate an alarm at a WP, you have to configure a block with:
1) One of the alarming options turned on (ie, HLOP = 1)
2) A group that includes the WP is selected for the configured alarm (ie,
HLGP = 1, 2 or 3 and the WP's letterbug is included in the compound's
devices for the selected group, or HLGP = 4, 5, 6, 7 or 8, and the WP's
letterbug is included in the Station's devices for the selected group).
3) An alarm priority is selected that is configured to have the horns sound,
often 1 or 2 (ie, HLPR = 1). Configuration for which alarm priority(s)
cause sound the alarm horn is done in the file /usr/fox/alarms/horn.cfg on
each WP.
The pan and tab files are for configuring the way the annunciator keyboards
function -- which LEDs are lit by which alarms, and which graphics are
called up by which key presses.
Please let me know if this answer is helpful. Also, let me know if you
would like some information on our System Configuration class which covers
these areas.
Regards,
Kevin FitzGerrell
Systems Engineer
Foxboro New Zealand
+64 9 573 7690
----- Original Message -----
From: "Khudhair, Waleed K" <waleed.khudhair@xxxxxxxxxx>
To: <foxboro@xxxxxxxxxxxxx>
Cc: <waleed.khudhair@xxxxxxxxxx>
Sent: Sunday, July 18, 2004 7:28 PM
Subject: [foxboro] Horn Configuration
> Hi all,
>
>
> Please, what is configuration required to produce "horn" at console in
> case of process alarm for specific point "block"? I have modified "tab"
> file under the directory "/usr/fox/alarms" and still the horn is not
> generated.
>
>
>
> Please advise.
>
> Thanks,
>
>
>
> _-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_-_
>
> Waleed K. Al-Khudhair
>
> Uthmaniyah Gas Plant
>
> Engineering Building
>
> Room 130
>
> DCS Administrator
>
> J 577-5396 Pager 870-1474
>
>
>
>
>
>
>
> _______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys Process
> Systems (formerly The Foxboro Company). Use the info you obtain here at
> your own risks. Read http://www.thecassandraproject.org/disclaimer.html
>
> foxboro mailing list: http://www.freelists.org/list/foxboro
> to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
> to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
>
>
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- References:
- [foxboro] Horn Configuration
- From: Khudhair, Waleed K
Other related posts:
- » Re: [foxboro] Horn Configuration
- » Re: [foxboro] Horn Configuration
- » Re: [foxboro] Horn Configuration
- [foxboro] Horn Configuration
- From: Khudhair, Waleed K