Re: [foxboro] GDEV freezing problem
- From: "Rick Rys" <Rys@xxxxxxxxxxxxxx>
- To: <foxboro@xxxxxxxxxxxxx>
- Date: Wed, 15 Dec 2004 00:13:12 -0500
The GDEV blocks are not connected directly to I/O. CIN blocks are used =
for
limit switch inputs and COUT blocks are used for Open and Close =
commands.
The I/O path is via a Gateway. The block looks like this:
NAME =3D COMPOUND:XV
TYPE =3D GDEV
DESCRP =3D=20
PERIOD =3D 1
PHASE =3D 0
LOOPID =3D=20
IOM_ID =3D=20
IP_FBM =3D 0
LM1_PT =3D 0
LM2_PT =3D 0
OP_FBM =3D 0
CO1_PT =3D 0
CO2_PT =3D 0
AVLLM1 =3D 1
AVLLM2 =3D 1
TOC =3D 2.0
DSRTRK =3D 1
ZDSOVR =3D 0
AUTDSR =3D 0
MANDSR =3D :XV.AUTDSR
INTDSR =3D :XZ.BO02
HLDDSR =3D 2
DSR_RB =3D 0
HLD =3D 0
INTLCK =3D :XZ.BO01
DISABL =3D 0
MA =3D :XV.MA.1
INITMA =3D 1
MANSW =3D 0
AUTSW =3D PATT:MCIN.CIN_14
MANFS =3D 0
SDWNOP =3D 0
INHOPT =3D 3
INHIB =3D SEQ.ACTIVE.~
INHALM =3D 0x0
ANM =3D=20
BAT =3D=20
BAP =3D 5
BAG =3D 4
SAP =3D 5
SAG =3D 8
IGNLM1 =3D 0
IGNLM2 =3D 0
DEVLM1 =3D :ZLC.CIN
DEVLM2 =3D :ZLO.CIN
INVLMT =3D 0
INVCO1 =3D 0
INVCO2 =3D 1
PLSOPT =3D 1
PLSTIM =3D 100
STAT1 =3D CLOSED
STAT2 =3D OPEN
STAT3 =3D CLOSING
STAT4 =3D OPENING
MM1 =3D FAIL TO CLOSE
MM2 =3D FAIL TO OPEN
MM3 =3D MISMATCH
MM4 =3D MISMATCH
MODE1 =3D DISABLE
MODE2 =3D INTERLOCK
MODE3 =3D MANUAL
MODE4 =3D HOLD
MODE5 =3D AUTO
USERL1 =3D 0
USERL2 =3D 0
END
The problem is reproducible by running a loadall on a test system. Once =
a
GDEV was frozen, rebooting the CP would not unfreeze it. It may be =
related
to installation issues as the plant was shutdown and the CP's =
initialized
and reloaded and I don't know the complete history of the control =
database,
but suspect certain iccdrvr/FOXCAE manipulations. I am not at the plant
site at the moment and need to investigate the reports of recent GDEV =
freeze
up's, as I cannot verify a spontaneous freeze, following the block
re-installation via "Delete and Undelete". Maybe a CAR is in order =
here.
Perhaps we found a GDEV bug or more likely we have some type of CP =
database
installation error.
Thanks,
Rick Rys P.E.
www.R2Controls.com
508-369-5186 Cell
508-339-6633 Home Office
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- Follow-Ups:
- [foxboro] I/A Batch 5.3 backups
- From: Ken . E . Moore
- Re: [foxboro] GDEV freezing problem
- From: Michael Kessler
- Re: [foxboro] GDEV freezing problem
- From: Jim Mowrey
- References:
- Re: [foxboro] GDEV freezing problem
- From: kevin . fitzgerrell
Other related posts:
- » Re: [foxboro] GDEV freezing problem
- » Re: [foxboro] GDEV freezing problem
- » Re: [foxboro] GDEV freezing problem
- » Re: [foxboro] GDEV freezing problem
- » Re: [foxboro] GDEV freezing problem
- » Re: [foxboro] GDEV freezing problem
- » Re: [foxboro] GDEV freezing problem
- [foxboro] I/A Batch 5.3 backups
- From: Ken . E . Moore
- Re: [foxboro] GDEV freezing problem
- From: Michael Kessler
- Re: [foxboro] GDEV freezing problem
- From: Jim Mowrey
- Re: [foxboro] GDEV freezing problem
- From: kevin . fitzgerrell