Brian, I have had good results with using the "TIM" function within a
calc block.
Here I use the first pulsed output to trigger "mailbox" blocks to store
the accumulated total, then the second pulse actually resets the
accumulators.
I'm sure this is not the most elegant way to do this, but I have
utilized this for many years.
Here are the steps I am using:
NOTE RI02: contains 86370.00000 - this causes the reset to occur 30
seconds before midnight
STEP01 TIM ; TIME IN SECONDS SINCE MIDNIGHT
STEP02 IN RI02 ; RESET TIME IN SECONDS
STEP03 SUB
STEP04 OUT RO01 ; TIME LEFT TO RESET IN SECONDS
STEP05 BIN 9 ; JUMP IF IT IS NOT TIME TO RESET
STEP06 IN 1 ; IF IT IS RESET TIME DO THIS
STEP07 STM M01
STEP08 GTO 11;
STEP09 IN 0 ; NO RESET
STEP10 STM M01
STEP11 LAC M01
STEP12 OUT BO01 ; RESET NOTIFICATION - in your case, this could be the
only thing you utilize
STEP13 OSP 4 ; LENGTH OF MAILBOX PULSE
STEP14 OUT BO02 ; LOAD MAILBOX PULSE
STEP16 DOFF 2 ; DELAY BETWEEN MAILBOX AND CLEAR PULSE
STEP17 NOT
STEP18 OSP 4 ; LENGTH OF CLEAR PULSE
STEP19 OUT BO03 ; CLEAR ACCUMS
STEP20 END
Have fun with it.
Sean Meltvedt
Flint Hills Resources Alaska LLC
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of BrianLong
Sent: Thursday, February 19, 2009 9:26 AM
To: Foxboro
Subject: [foxboro] Follow-up ACCUM reset and Question
The original problem was trying to get an ACCUM block in two different
CP's to reset at the same time. In our case setting the ACCUM blocks as
the first block in the compund in each CP and using the same calc block
for the reset seemed to take care if it. There is about a 1 second
difference now.
New question, we're using a CALC block to reset the ACCUM blocks using
xxCPxx_STA:STATION.HOUR and .MINUTE parameters. The reset is set to
occur at 23:58, looking a values in the historian the reset will occur
anywhere between 23:58:08 and 23:58:16. This is not an issue but I was
curious why it takes that long to process?
Thanks,
Brian Long
Arkansas Kraft
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: