I have recently experienced this problem when using Coax/Fiber =
converters with the CP60's. When I had a Coax/Fiber converters fail =
that was on the CP60 side (converting from CP60 Fieldbus Coax to Fiber) =
I started receiving these types of alarms with the shadow CP becoming =
unmarried. It would not marry up again either. Problem ended up be =
that with the bad Coax/Fiber converter the processors were supposedly =
seeing a mismatch in the number of I/O modules attached to the =
processors. The problem can be identified by temporarily disable the B =
fieldbus and see if the processor will marry back. If it does you have =
problem on the B fieldbus.
Regards,
James Mueller
Cleveland Cliffs Michigan Operation
Senior Process Control Engineer
Work (906) 475-3534
Fax (906) 475-3538
JDMueller@xxxxxxxxxxxxxxxxxxxx
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] =
On Behalf Of Jeff Hurt
Sent: 14 July, 2008 8:10 AM
To: foxboro@xxxxxxxxxxxxx
Subject: Re: [foxboro] Failed CP60
Yes, both of the red and green LED's are illuminated on the failed CP. =
Looking at the alarm printout, here is what I see:
=20
Single PIO Bus Access Error on B
Single PIO Bus Access Recovery on B
FCM B module failed
FCM B no longer failed
=20
These have came in multiple times.
=20
Thanks,
Jeff H
=20
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process =
Systems (formerly The Foxboro Company). Use the info you obtain here at =
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
=20
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
=20
#########################################################################=
######
This electronic message and any attachments included with this message =
are for the exclusive use of the individual or entity to which it is =
intended to be addressed. This message may contain information that is =
privileged or confidential and thereby exempt and protected from =
unauthorized disclosure under applicable law. If the reader of this =
message is not the intended recipient, or an employee or agent =
responsible for delivering the message to the intended recipient, be =
aware that any disclosure, dissemination, distribution or copying of =
this communication, or the use of its contents, is not authorized and is =
strictly prohibited. If you have received this communication and are not =
the intended recipient, please notify the sender immediately and =
permanently delete the original message from your e-mail system.=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- References:
- Re: [foxboro] Failed CP60
- From: Jeff Hurt
Other related posts:
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- » Re: [foxboro] Failed CP60
- Re: [foxboro] Failed CP60
- From: Jeff Hurt