Re: [foxboro] CP60 vs IEC61508 safety requirements
- From: Corey R Clingo <corey.clingo@xxxxxxxx>
- To: foxboro@xxxxxxxxxxxxx
- Date: Thu, 5 Nov 2009 08:45:29 -0600
Doubtful, for the mature CP60 for sure, and probably the CP270, too. Most
DCS/PLC/generic controller hardware is not designed to have high SFF and
low PFD. For this and other reasons, the relevant industry standards
limit the risk reduction "credit" you can take for a "basic process
control system" to a factor <=10.
Triconex, Hima, Honeywell FSC, several other "safety PLCs", are
purpose-built for this sort of thing. If you need more than that
factor-of-10 risk reduction from a programmable system (e.g., SIL1 or
greater), you should be using something of their ilk.
Corey Clingo
BASF Corp.
Aymen LAZAAR <aymen.lazaar@xxxxxxxxx>
Sent by: foxboro-bounce@xxxxxxxxxxxxx
11/05/2009 12:54 AM
Please respond to
foxboro@xxxxxxxxxxxxx
To
foxboro <foxboro@xxxxxxxxxxxxx>
cc
Subject
[foxboro] CP60 vs IEC61508 safety requirements
Hi all,
I'm interested to know if there was any tentative to certify the 60 CPs to
IEC61508 safety requirements, even through a proven-in use analysis/study.
One more thing am interested in is PFD, SFF andfailure statistics for
this
kind of CPs
Thanks,
Aymen
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts: