Daniele
This may not be of much help but we get
K0MG03 Error Protocol FTXSS 000080 Memory violation occured 00006C09A05F
On an intergrator 30 for Modbus Pluss, it happens when another device on
the MB+ network sends a command to the Gateway. (eg network device
discovery scan)
It looks like you are having the problem with a CP60 but you mention a
PLC so there must be a ?FBM224.
In our case the gateway memory dumps and takes 10 minutes to come back
online
Shaun
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx]
On Behalf Of Daniele Tocco
Sent: Tuesday, 17 October 2006 05:57
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] CP Error protocol
Hi all it is already 3 time that I got problems with one CP of the
plant.
It seems that the CP looses the comunication with the I/O interfaces.
The syslog error is the following:
CP6002 Error protocol FTXSS 00080 Memory violation occurred 00006C17130F
CP6002 Error protocol FTXSS 00080 Memory violation occurred 00006C171B68
CP6002 Error protocol FTXSS 00080 Memory violation occurred 00006C17130F
CP6002 Error protocol FTXSS 00080 Memory violation occurred 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
CP6002 Error protocol 1 1 No Msg found 00006C171B68
AW7001 Process=3DNFD000001 NF8023-00001 NB Cable test to WP7002 OK. No
response from CP6002
There is also a MC I/O error that has been logged 13 minutes before
this. It trasduces the PLC signals in DCS signals. Could be this device
too to create the out of service of CP6002?
Somebody can give me some hints?
Thank you very much
Daniele
=20
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
=20
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
=20
=0A=0ANOTICE - This message and any attached files may contain informatio=
n that is confidential and intended only for use by the intended recipien=
t. If you are not the intended recipient or the person responsible for de=
livering the message to the intended recipient, be advised that you have =
received this message in error and that any dissemination, copying or use=
of this message or attachment is strictly forbidden, as is the disclosur=
e of the information therein. If you have received this message in error =
please notify the sender immediately and delete the message.
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- Follow-Ups:
- Re: [foxboro] CP Error protocol
- From: Daniele Tocco
Other related posts:
- » Re: [foxboro] CP Error protocol
- » Re: [foxboro] CP Error protocol
- » Re: [foxboro] CP Error protocol
- » Re: [foxboro] CP Error protocol
- Re: [foxboro] CP Error protocol
- From: Daniele Tocco