Re: [foxboro] CMP:BLK

You can turn off processing or inhibit alarms at the compound level. 
Judicious choice of block grouping in compounds may enable you to take 
advantage of these capabilities.
I have been told that the compound and block lists are scanned in a linear 
fashion to see if they are slated for processing in a particular BPC.  You 
might save some scanning of some blocks by phasing the compounds, as 
blocks in a compound are skipped if that compound is not scheduled for 
execution in a particular BPC.  In my experience, though, this makes block 
configuration too inflexible; we set all the compounds to period 1, phase 
0 except in certain situations (e.g., in some gateways where the compound 
scheduling can have an effect on scanning frequency of the foreigh 
device).  If we come close to overloading a CP, we get a bigger one or 
split it up.

Corey Clingo
BASF Corporation





"Terry Currie" <TCurrie@xxxxxxxxxx> 
Sent by: foxboro-bounce@xxxxxxxxxxxxx
06/14/2006 09:01 AM
Please respond to
foxboro@xxxxxxxxxxxxx


To
<foxboro@xxxxxxxxxxxxx>
cc

Subject
[foxboro] CMP:BLK






We have started to program a new CP60.
My question, is there a limit to the number of compounds?
Is it better to have few cmp with lots of blks, or lots of cmps each
with a few blks?

Terry





 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             http://www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: