Re: In our plant the operator select an C:B.P with $PICK1 an then he will
change the value. So it isn't possible to give the right range for each
Point.

The correction configuration approach is to configure the pick point with
the range.

So, instead of configuring C:B.P, you would configure C:B.P|R=<low>,<high>.

I will admit that this could be a lot of work if you have a lot of displays
to update. You could use d_edit (DM) or dedit (FV) to make the change more
quickly.

Other than this approach, I'm not aware of anything in FV/FD to do what you
want.


Regards,
 
Alex Johnson
Invensys Process Systems
Invensys Systems, Inc.
10707 Haddington
Houston, TX 77043
713.722.2859 (voice)
713.722.2700 (switchboard)
713.932.0222 (fax)
ajohnson@xxxxxxxxxxx

-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On
Behalf Of Hegewisch, Dirk
Sent: Friday, February 18, 2005 1:40 AM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] AW: Increment Values

Hi,
thanks for your answer, but that isn't an good solution for me.

I try to describe it better:
In our plant the operator select an C:B.P with $PICK1 an then
he will change the value.
So it isn't possible to give the right range for each Point.

I am looking for an solution that only increase/decrease (any value)
with an fix value. Like +/- 0.5.
And it doesn't care if we have %, =B0C, t, m=B3/h, .... or what ever.

Regards,
 Dirk

-----Urspr=FCngliche Nachricht-----
Von: Johnson, Alex (Foxboro) [mailto:ajohnson@xxxxxxxxxxx]=20
Gesendet: Donnerstag, 17. Februar 2005 01:07
An: foxboro@xxxxxxxxxxxxx
Betreff: Re: [foxboro] Increment Values

The key is the use of a range or Range Variable (Rxy).

The Range Variables (Rxy) parameters are OM objects that contain 3 =
floating
point values.

Rxy[0] - High scale - HSCxy
Rxy[1] - Low scale - LSCxy
Rxy[2] - Change Delta - DELTxy

The DM/FV is smart enough to set the big (double arrow) and small =
(single
arrow) ramp buttons to a percentage of the span IF the Rxy parameter is
specified on the tag name, e.g.,

C:B.SPT|RI1

Might be used for a PIDA block setpoint ramp.


If the Rxy parameter is not specified, a default is assumed and the RAMP
Buttons will use a percentage of that span.

If you want a custom span, you can specify it as follows:

C:B.P|R=3D<lowRng>,<hiRng>


So, try this:

Make a graphic that contains a rectangle. Configure the select action =
ramp
with the following line:
=20
C:B.SPT|R=3D2.0,98.0

Protection Class: 0

+/- percent control range: 5

Where C:B.SPT refers to some PID block setpoint in your system.

This configuration will clamp the .SPT between  2.0 and 98.0 Obviously =
the
custom range should be within the block's RI1 (LSCI1,HSCI1)

****** Thanks to Leo Moramarco/FoxCanada and Ignacio Queirolo =
Olivera/Repsol
for some of the material above.


Regards,
=20
Alex Johnson
Invensys Process Systems
Invensys Systems, Inc.
10707 Haddington
Houston, TX 77043
713.722.2859 (voice)
713.722.2700 (switchboard)
713.932.0222 (fax)
ajohnson@xxxxxxxxxxx
-----Original Message-----
From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] =
On
Behalf Of Hegewisch, Dirk
Sent: Wednesday, February 16, 2005 8:28 AM
To: foxboro@xxxxxxxxxxxxx
Subject: [foxboro] Increment Values

Hi Group.

I want change the value of an given C:B.P.
The value should change up/down from current value.
For example in +/-0.5 steps   (newvalue =3D3D oldvalue + 0.5)

The ramp function isn't the right function. Because the C:B.P increase
by percent of the control range.

Has anybody an easy solution for this small problem?

Dirk

=20
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
=20
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe:      =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
=20

=20
=20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
=20
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
to unsubscribe:      =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
=20
 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

 
 
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
 
foxboro mailing list:             //www.freelists.org/list/foxboro
to subscribe:         mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe:      mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
 

Other related posts: