Hi List, I was shocked while reading the Release Notes 6.5.1. Problem: If the INHPRT parameter is set to 1 in the STATION block, a problem occurs where process alarm messages are not sent to the alarm printer attached to a communication server. Consecutive alarm messages that are destined to the communication server are packaged into one IPC message. If one of the alarm types in this IPC message is an ALARM_ENABLE or ALARM_DISABLE type, and INHPRT =3D 1, the communication server discards all the messages, and both the process alarms and the alarm inhibit/uninhibit messages are not printed. Resolution: This problem is corrected with V6.5.1 I/A Series software. ... I prepare an upgrade from V6.1.1 to V6.5 because our alarm manager = instructed me to disable ALARM_ENABLE/DISABLE messages. It seems to be a great risk setting the INHPRT parameter to 1 and I'm = not able using V6.5.1 due to the fact that the system runs on a Style C. Questions: - What is a communication server? Is it a COMM (communication = processor)? - What kind of software has to fixed to get a solution on V6.5? Is it necessary to change the COMM-image or the AW-software? Regards, Andreas ------------------------------------ Deutsche BP Aktiengesellschaft Chemicals Production Koeln Abt. PLS Andreas Weiss Geb. Q01 Alte Str. 201 50769 Koeln Tel.: +49-2133-55-7804 Fax: +49-2133-55-7583 mailto:andreas.weiss@xxxxxxxxx _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave