[foxboro] SPD_CAP SELECTION
- From: Jalil Saeidzadeh <jalil.saeid@xxxxxxxxx>
- To: foxboro@xxxxxxxxxxxxx
- Date: Thu, 26 Jan 2006 18:47:59 +0300
List,
Using a CALC block, I am trying to develop logic for capacity/speed
selection of a compressor. What I am doing is as following:
BIO1 : SPEED SELECT FBK
BI02 : LOCAL/REMOTE SELECTION FBK
BI03 : CAPACITY SELECT FBK
BI04 : SPEED/CAPACITY TOGGLE SIGNAL (OPERATOR ACTION)
STEP01 = CST
STEP02 = IN BI02
STEP03 = BIF 25 ; COMPRESSOR IS ON LOCAL DONOT DO ANYTHING
STEP04 = IN ~BI04 ; OPEARATOR NOT TOGGLE THE INPUT
STEP05 = IN BI03 ; CAPACITY SELECT FBK IS 1
STEP06 = AND 2
STEP07 = BIF 11 ; GO AND CHECK THE 2ND CONDITION
STEP08 = CLR BO01 ; SPEED TRACKING
STEP09 = SET BO02 ; CAPACITY SELECT
STEP10 = GTO 27 ; GO TO END
STEP11 = IN BI04 ; OPERATOR TOGGLE THE INPUT
STEP12 = IN BI03 ; CAPACITY SELECT FBK IS 1
STEP13 = AND 2
STEP14 = BIF 18 ; GO AND CHECK THE 3RD CONDITION
STEP15 = SET BO01 ; SPEED SELECT
STEP16 = CLR BO02 ; CAPACITY TRACKING
STEP17 = GOT 27 ; GO TO END
STEP18 = IN BI04 ; OPERATOR TOGGLE THE INPUT
STEP19 = IN BI01 ; SPEED SELECT FBK IS 1
STEP20 = AND 2
STEP21 = BIF 27 ; NO COMMAND ISSUED GO TO END
STEP22 = CLR BO01 ; SPEED TRACKING
STEP23 = SET BO02 ; CAPACITY SELECT
STEP24 = GTO 27 ; GO TO END
STEP25 = CLR BO01; WHEN COMPRESSOR IS IN LOCAL BOTH SPEED AND
STEP26 = CLR BO02; CAPACITY WOULD TRACK ONLY
STEP27 = END
Is there better idea for doing the same? The logic is based on the
following:
1. When compressor is on local both speed and capacity should track
only (start-up).
2. When compressor switched to remote capacity is default mode of
control.
3. When compressor is on capacity control and lost the capacity
feedback (for any reason) there should be no change in status.
4. When compressor is on speed control and lost the speed feedback
(for any reason) there should be no change in status.
5. If for any reason compressor switched over to local control, set
both speed and capacity to track only.
6. Speed or Capacity selection would be by operator request only.
Regards,
Jalil Saeidzadeh
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts:
- » [foxboro] SPD_CAP SELECTION