[foxboro] Read back feature of FBM233 with OPC
- From: Joachim Leuker <leuker@xxxxxxxx>
- To: foxboro@xxxxxxxxxxxxx
- Date: Fri, 17 Oct 2008 22:22:16 +0200
Hi list,
the output blocks IOUT, ROUT and PAKOUT work with a read back feature
in the FBM233. At least they do this when used in an OPC interface.
We connected a Siemens S7 PLC to a FBM233. We found out that it is
possible to manipulate a value of a ROUT or IOUT block from both sides.
If the value is changed in the PLC, then it also changes in the ROUT
block.
We also need some bit values to be set in the PLC or in the I/A system.
We observe a strange behaviour there:
1) We set bit IN1 in the PAKOUT
2) We set bit #2 in the PLC, and the bit is also set in the PAKOUT. It
looks the same as bit #1 in the detail display.
3) Then we set IN3 in the PAKOUT. The change made earlier to bit #2 is
reversed and only IN1 and IN3 are set.
Another strange thing is that if I set IN32, the PAKOUT is frozen and
no change can be made to it.
I deleted the PAKOUT and put an IOUT to the same OPC address. I made no
change on the PLC side. Then I could make bit changes on both sides as
expected and I could also set bit #32.
I/A version is 8.2, the CP is a FCP270.
Is this a configuration error or an error in the PAKOUT block?
Regards,
Joachim Leuker
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
- Follow-Ups:
- Re: [foxboro] Read back feature of FBM233 with OPC
- From: Ron Schafer
Other related posts:
- » [foxboro] Read back feature of FBM233 with OPC
- Re: [foxboro] Read back feature of FBM233 with OPC
- From: Ron Schafer