[foxboro] Micro I/A upgrade to 6.2.1
- From: "Lowell, Tim:" <tlowell@xxxxxxxx>
- To: "'foxboro@xxxxxxxxxxxxx'" <foxboro@xxxxxxxxxxxxx>
- Date: Fri, 19 Oct 2001 12:40:50 -0700
List,
We had another fun day with Micro I/A today. We have 3 Micro I/A =
stations
connected to Allen-Bradley Remote I/O thermocouple modules all =
throughout
the refinery. They routinely drop off-line at all hours, prompting =
someone
to physically unplug the modules and then put the plugs back in to =
reboot.
To remedy this problem, Foxboro offered us version 6.2.1 of the Micro =
I/A
image. =20
Well, today we loaded the new image, initialized the Micro I/A's, =
loaded
their databases back, and...every single temperature was 15-20=B0F too =
high!
Our service guy made frantic calls to TAC and various other service =
guys,
and got no useful answers. So, I'm sitting there, cursing Foxboro, =
berating
myself for even letting them in the refinery on a Friday, when I start
reading the Micro I/A 6.2.1 manual a little closer. Buried somewhere =
deep
in the manual, and certainly not in big bold letters in the Release =
Notes,
is a table listing the HSCO1 and LSCO1 values that you need to enter =
for
each AIN block that you create to attach to a thermocouple so you can =
read
it. THEY HAD CHANGED THE LSCO1'S ON TYPE J AND K THERMOCOUPLES!!! =
They
used to be -319 and -382, now they are -346 and -454. So, I do an
iccdrvr.tsk and change all the LSCO1's on all the AIN blocks, and =
presto, I
have the right readings again.
I'm not sure where to begin with this. Does anyone in FoxMass actually =
test
these upgrade procedures? How could Foxboro possibly modify the =
control
database to the point where the millivolt signal (on the two most =
common
thermocouple types, no less) coming in before the upgrade will not
correspond to the same temperature reading after the upgrade, and not
consider this significant? I am flabbergasted.
For those of you on the list who have been cursed with this combination =
of
hardware, please remember to change the LSCO1's on the AIN blocks when =
you
upgrade to the 6.2.1 image.
Tim Lowell
Control Systems Engineer
Phillips Petroleum Company, Trainer Refinery
Phone: 610-364-8362
Fax: 610-364-8211
tlowell@xxxxxxxx
___________________________________________________________________
This list is neither sponsored nor endorsed by The Foxboro Company.
Use the information obtained here at your own risk. For disclaimer,
see http://www.thecassandraproject.org/disclaimer.html#maillist
list info: http://www.freelists.org/list/foxboro
subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts:
- » [foxboro] Micro I/A upgrade to 6.2.1