The equation I gave (with P in the numerator and T in the denominator) is
used for mass flow compensation. Doing it this way essentially multiplies
your compensated flow by density to give you a result in terms of mass.
Since you asked for SCFM, I assumed that this was what you wanted. (For
ideal gasses with constant composition, standard volume units are
proportional to mass.)
If you are doing custody transfer or attempting to come up with a result
that's proportional to the heat content of the natural gas, then a mass
flow is what you want.
Greg Hurwitt
----- Forwarded by Gregory A Hurwitt/NCF/FREEPORT/BASF-CORP/BASF on
02/28/2008 02:12 PM -----
Gregory
A
Hurwitt To
<gregory foxboro@xxxxxxxxxxxxx
.hurwitt cc
@basf.co
m> Subject
Sent by: Re: [foxboro] Natural Gas Temp &
foxboro- Pressure compensation
bounce@f
reelists
.org
02/28/20
08 01:38
PM
Please
respond
to
foxboro@
freelist
s.org
The following is based on ideal gas approximation and flows measured by
differential pressure. It will work well for natural gas, nitrogen, air,
etc. Do not use it for steam.
First, as is always the case for flows measured via differential pressure,
make sure you are performing exactly one square root extraction on the D/P
signal to read volumetric (uncompensated) flow. This square root
extraction can be configured in the transmitter, or via use of SCI = 5 in
your AIN block, but not both at the same time.
Next, Compensation factor = sqrt ( (P/Pd) * (Td/T) ), where:
P = measured pressure (absolute units)
Pd = design pressure (absolute units)
Td = design temperature (absolute units)
T = measured temperature (absolute units)
To determine design temperature/pressure, look at the spec sheet and/or
flow calculation for the flow element.
To convert units to absolute:
deg R = deg F + 459.6
psia = psig + 14.7
Your final compensated flow is the uncompensated flow times the
compensation factor.
Greg Hurwitt
BASF Corp.
Freeport, TX
David
Johnson
<drjohn@ To
hiwaay.n Foxboro@xxxxxxxxxxxxx
et> cc
Sent by:
foxboro- Subject
bounce@f [foxboro] Natural Gas Temp &
reelists Pressure compensation
.org
02/28/20
08 01:04
PM
Please
respond
to
foxboro@
freelist
s.org
Hello all,
I was wondering if someone had the formula in their back pocket for
taking a DP on a natural gas line and converting it to a compensated flow.
I have a DP orifice plate that is scaled from 0-235 " water.
This, I
am told corresponds to 0-2000 CFM.
I have a PT scaled from 0-130 PSI
I have a TT scaled from 0-300 deg F.
So a DP of 100" H2O at 80 Deg F and 100 PSI is ??????SCFM.
So can one of you Chemical Engineers lend a hand?
Thanks,
David
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts:
- » [foxboro] Fw: Natural Gas Temp & Pressure compensation