Imran, The AB Gateway (or Integrator30) limiting resource is usually the RS232 baud rate, likely 19, 200. Each serial communication consists of overhead (addresses, security check, etc) that do not provide information about your process and data (your process good stuff) that all must be part of the 19,200 baud. You need to try and minimize the overhead by reading (or writing) contiguous bytes of PLC data. Most users get the PLC logic to move the various pieces of information in the PLC into contiguous data areas in the PLC and then the Foxboro Integrators read that contiguous data with the largest read that is possible. If you just read your input data directly, most of your 19,200 baud would be overhead. It takes a little work to map the data in and then read it out on the Foxboro side but it is well worth the effort. At 19,200 baud you can usually read about 350 bytes per second of your data but there are a lot of other factors (like the number of PLC's on your DH+ network) that could lower this 350 bytes per second. Also you need to keep writes from the Foxboro to the PLC to low numbers per second. ________________________________ De: foxboro-bounce@xxxxxxxxxxxxx de la part de Miller, Jeff Date: ven. 2007-09-14 18:44 À: foxboro@xxxxxxxxxxxxx Objet : Re: [foxboro] Communication problem b/w FBM231 & AB PLC Imran, The B3 file is located in the PLC5. You have to configure the file and set the number of words that you will need to transfer the data. We get the data into the B3 table by using the ladder logic to write the input or output to the B3 bit. Example 4.8:O goes to B3:1.1 etc. I believe you could also use a data transfer block to send several words at one time from the input or output file to the B3 file. =20 JAM Our system is currently using AB KF2 converters to go from DH+ to RS-232 and a Comm 15 module. -----Original Message----- From: foxboro-bounce@xxxxxxxxxxxxx [mailto:foxboro-bounce@xxxxxxxxxxxxx] On Behalf Of Imran Waheed Butt Sent: Thursday, September 13, 2007 10:12 AM To: foxboro@xxxxxxxxxxxxx Subject: Re: [foxboro] Communication problem b/w FBM231 & AB PLC Dear All, The communication issue is resolved by changing the DIP switch settings of CAM and by putting the correct CAM address in ECB 201. But the point numbers are we cant translate to the format of BIN or RIN blocks we don't understand the format Like B3:4/6 the file B3 what and where is this file and how to translate the 4.8:0 to above format. you can see the details in at the end of this e-mail. Previously AIN, AOUT, CIN and COUT blocks are in the database of DI15 which communicate with PLC, and now these blocks we can't use with FBM231 to communicate with PLC so, we create RIN, ROUT, BIN and BOUT blocks and connect the out put of these blocks to the input of AIN and CIN and output of COUT and AOUT to input of BOUT and ROUT. Now problem is that the previous addressing of PNT parameter of CIN is and COUT are like 4.12:0 and 16.15:0 and for AIN and AOUT have like 126:0 at their PNT parameter. Kindly guide me how to translate the above format to PNT parameter to the format of BIN,BOUT, RIN and ROUT. We copy the same PNT no. to the PNT of BIN, BOUT, RIN, ROUT's PNT but when loaded to FCP it gives error W65. If and one experience the same issue kindly guide me On 9/13/07, Kevin Fitzgerrell <fitzgerrell@xxxxxxxxx> wrote: > > Imran, > > You need to know which CAM you have. There will be an AB part number > on the device your serial cable from the Foxboro switch block plugs in > to. What is it? > > Regards, > > Kevin FitzGerrell > > On 9/12/07, Imran Waheed Butt <butt.imran@xxxxxxxxx> wrote: > > Dear Scott, > > I have that document and I followed that and switch setting which you > > provide does not work and we don't know the modem numebr but the modem > is > > also of AB and AB PLC is PLC 5/40 and it is connect to CAM or Modem by > DH+, > > > > and we configured the .XML file as > > > > Port 1 > > Mode=3D RS-232 > > Baud Rete=3D9600 > > Parity=3D none > > stop bits=3D1 > > databits=3D8 > > driver=3DDHPlus/CRC > > > > Kindly guide me. > > > > Thanks and Rgds > > Imran Butt. > > > > > > > _______________________________________________________________________ > This mailing list is neither sponsored nor endorsed by Invensys Process > Systems (formerly The Foxboro Company). Use the info you obtain here at > your own risks. Read http://www.thecassandraproject.org/disclaimer.html > > foxboro mailing list: //www.freelists.org/list/foxboro > to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin > to unsubscribe: mailto: foxboro-request@xxxxxxxxxxxxx?subject=3Dleave > > Dear All, Our customer is upgrading the I/A version form V4.3 Unix to V8.2 on XP and previous system has CP30FT communicating with 100 series FBMs and FBCs and quantity 3 DI15 gateways communicating with Allen Bradley PLC through CAM or Modem which is provided by Allen Bradley. The CP30FT is upgraded to FCP270FT and 100 series FBM and FBC are remain same. The 3 no. DI15 are replaced by and other FCP270FT with FBM231 (FT). I am at the commissioning/installation of the system and facing following problems, 1. FBM231 is not communicating with AB PLC through CAM or Modem as we translate the same DIP switch setting which is on the P0970VN (DI15 configuration selection switch) to the FBM231 TA, the switch settings are as, DI15>>> SW1-1,2,3,4,7,8 & SW2-1,3,4,6,8 are closed and remaining are open we translate them form documents B0193RL-Rev H page 49-50 and form B0700AH Rev E page 62-63 and translated switch setting are as, FBM231 TA>>> A-2,4,6,8 & B-4,8 & C-1 are close and remaining are open. But it is not communicating with PLC. 2. The cable part number which is connecting PLC to Gateway is P0970WY-C and we are using the same cable. 3. Previously AIN, AOUT, CIN and COUT blocks are in the database of DI15 which communicate with PLC, and now these blocks we can't use with FBM231 to communicate with PLC so, we create RIN, ROUT, BIN and BOUT blocks and connect the out put of these blocks to the input of AIN and CIN and output of COUT and AOUT to input of BOUT and ROUT. Now problem is that the previous addressing of PNT parameter of CIN is and COUT are like 4.12:0 and 16.15:0 and for AIN and AOUT have like 126:0 at their PNT parameter. Kindly guide me how to translate the above format to PNT parameter to the format of BIN,BOUT, RIN and ROUT. We copy the same PNT no. to the PNT of BIN, BOUT, RIN, ROUT's PNT but when loaded to FCP it gives error W65. Kindly all the experts provide me solution of above issues. Thanks and Best Regards, Imran Butt, System Engineer, Manstock. =20 =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html =20 foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin to unsubscribe: = mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave =20 _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave -- No attachments (even text) are allowed -- -- Type: application/ms-tnef -- File: winmail.dat _______________________________________________________________________ This mailing list is neither sponsored nor endorsed by Invensys Process Systems (formerly The Foxboro Company). Use the info you obtain here at your own risks. Read http://www.thecassandraproject.org/disclaimer.html foxboro mailing list: //www.freelists.org/list/foxboro to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave