Daren,
for non redundant integration of Modbus to CP40 nodes we also used =
"nacked"
Micro I/A as shown in PSS 21H - 7C1 B3.
Regards
Heinz Maurer
Vertriebsbuero Duesseldorf
Invensys Systems GmbH
Heerdter Lohweg 53-55
40549 Duesseldorf
Germany
Tel.: +49 (0) 211 5966 -333
Fax.: +49 (0) 211 5966 -300
Mob.: +49 (0) 173 25 32 515
Email: heinz.maurer@xxxxxxxxxxxx
http://www.invensys-process-systems.de
> -----Urspr=FCngliche Nachricht-----
> Von: Daren Bishop [SMTP:dbisho@xxxxxxxxxxxx]
> Gesendet am: Mittwoch, 11. Dezember 2002 19:04
> An: foxboro@xxxxxxxxxxxxx
> Betreff: Re: [foxboro] Modbus FBM, was "Back to forcing an ABSCAN to=20
>=20
>=20
> Marcel,
> =20
> =20
> *************************************************************
> =20
> Smaller....OK. Point?
> =20
> Cheaper....OK. How much?
> =20
> Faster(etc)OK. So can/is Modbus Plus (1.5MB/s).. but that got =
canxed.
> =20
> Many manufacturers are now moving away from the RS232 and RS485
> serial=20
> links as standard features, and you have to buy a additional =
comm
> card=20
> to handle this. There went your price reduction, you just had =
to=20
> spend the money somewhere else.
> =20
> I understand that the new FBM is better than the old
> integrator(that's=20
> fine and good).. but you can only use it with CP60's which kills =
it's
>=20
> usefulness. (Saying I have CP40B's and need to integrate =
Modbus.) Now
>=20
> one has to buy a CP60???? No price break there.
> =20
> To the point... What is and has been needed for some time now is =
a=20
> "Integrator" or FBM that works with ANY AND ALL CP combinations =
that=20
> talks Modbus over TCP/IP!!!
> =20
> Regards,
> =20
> ______________________________ Reply Separator=20
> _________________________________
> Subject: [foxboro] Modbus FBM, was "Back to forcing an ABSCAN to =
writ
> Author: <foxboro@xxxxxxxxxxxxx> at INTERNET-MAIL
> Date: 12/11/02 11:44 AM
> =20
> =20
> =20
> Hi,
> =20
> > I thought one of the new Modbus FBM's was Modbus/TCPIP..=3D20 =
> which
>=20
> is still "serial" but at a greater throughput?=3D20
> =20
> No, it supports serial links (RS232 and RS485) with up to 115kBit/s =
as =3D=20
> far
> as I know.
> =20
> > If not.. the ONLY advantage would be the flexability of=3D20=20
> > locations that the device could be installed,=3D20
> =20
> No, it's much smaller than an integrator 30, cheaper, faster and =3D=20
> supports
> direct transmission of floating point values in a 4-Byte format =3D=20
> (compatible
> to the Triconex Modbus implementation), so that no conversion loss=20
> (float-integer-float) is existing anymore.
> =20
> That's cool. ;-)
> =20
> Best regards -
> =20
> Marcel Sieling
> Systems Technologies
> =20
> Invensys Systems GmbH
> Heerdter Lohweg 53 - 55
> 40549 Duesseldorf
> Germany
> Tel.: +49 (0)30-267-15542
> Tel.: +49 (0)211 5966-171
> Fax: +49-(0)172-50-2673077
> Mobile: +49-(0)172-2673077
> Email: <mailto:msieling@xxxxxxxxxxx>=3D20=20
> Homepage: <http://www.foxboro-deutschland.de>=3D20
> Visit my private (german) homepage: <http://www.powerslider.de>=3D20
> =20
> =20
> =20
> > -----Urspr=3DFCngliche Nachricht-----
> > Von: Daren Bishop [mailto:dbisho@xxxxxxxxxxxx]=20
> > Gesendet: Dienstag, 10. Dezember 2002 19:30
> > An: foxboro@xxxxxxxxxxxxx
> > Betreff: [foxboro] Re[2]: Back to forcing an ABSCAN to write, =
etc=3D20=20
> >=3D20
> >=3D20
> >=3D20
> > Alex,
> > =3D20
> > I thought one of the new Modbus FBM's was Modbus/TCPIP..=3D20=20
> > which is still "serial"
> > but at a greater throughput?=3D20
> >=3D20
> > If not.. the ONLY advantage would be the flexability of=3D20=20
> > locations that the=3D20
> > device could be installed, and all we have is the old=3D20=20
> > "Mountain and Mohammed"=3D20
> > scnenario! In other words.. if you don't move forward, it's a=3D20=20
> > waste of time and=3D20
> > money. Just another device that doesn't improve performance.=20
> >=3D20
> > Hopefully for David's sake the AB Integrator FBM will be=3D20=20
> > ethernet or DH+ direct.
> >=3D20
> >=3D20
> >=3D20
> > ______________________________ Reply Separator=3D20=20
> > _________________________________
> > Subject: Re: [foxboro] Back to forcing an ABSCAN to write, etc=3D20 =
> > Author: <foxboro@xxxxxxxxxxxxx> at INTERNET-MAIL
> > Date: 12/10/02 1:00 PM
> >=3D20
> >=3D20
> > =3D20
> > Well, there's a Modbus FBM coming shortly for CP-60s under=3D20=20
> > V6.5. Still it is=3D20
> > only serial and only Modbus.
> > =3D20
> > =3D20
> > FBMs for other PLCs and physical layers are in the mill, but ...=20
> > =3D20
> > =3D20
> > Regards,
> > =3D20
> > Alex Johnson
> > Invensys
> > 10707 Haddington
> > Houston, TX 77063
> > 713.722.2859 (office)
> > 713.722.2700 (switchboard)
> > 713.932.0222 (fax)
> > ajohnson@xxxxxxxxxxx <mailto:ajohnson@xxxxxxxxxxx>=3D20=20
> > For the latest information on ArchestrA, go to=3D20
> > www.invensys.com/Archestra.html
> > <http://www.invensys.com/divisions/Archestra.html> .=20
> > =3D20
> > =3D20
> > -----Original Message-----
> > From: David Johnson [SMTP:DRJohn@xxxxxxxxxx]=3D20=20
> > Sent: Tuesday, December 10, 2002 11:43 AM=3D20
> > To: foxboro@xxxxxxxxxxxxx
> > Subject: [foxboro] Back to forcing an ABSCAN=3D20=20
> > to write, etc
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > If there is not a way to force a write of the data=3D20=20
> > table in event
> > driven=3D20
> > mode, there should be!
> > =3D20
> > I can save a tremendous amount of my serial bandwidth=3D20=20
> > between I/A
> > and the=3D20
> > KF2 if I only write values to the PLC when they=3D20=20
> > change. I may have
> > a set=3D20
> > of timer values that change once a week or less. The=3D20=20
> > longest period
> > listed=3D20
> > in the book is 1024 seconds. That would be OK in a=3D20=20
> > polled situation
> > except=3D20
> > if the operator changes a setpoint from an I/A screen=3D20=20
> > it might take
> > more=3D20
> > than 16 minutes for the change to be reflected in the=3D20=20
> > system. Not
> > good.
> > =3D20
> > So we go look at event driven mode. Values are=3D20=20
> > written to the PLC
> > only if=3D20
> > a change is made to the input side of the data. Changes =
are=20
> > transferred to=3D20
> > the PLC at the time that the operator makes the=3D20=20
> > changes. Very good.
> > BUT,=3D20
> > suppose the PLC reboots, or fails in some other way=3D20=20
> > that changes our
> > =3D20
> > values. Unless we change the input side of the=3D20=20
> > block, no write will
> > =3D20
> > occur. So what we want to do is check a heartbeat=3D20=20
> > signal and when=3D20
> > communication resumes after any absence force a write=3D20=20
> > of all the
> > data in=3D20
> > the event driven tables. Then everything will be=3D20=20
> > synced up. I
> > can't find=3D20
> > a mechanism to do this.
> > =3D20
> > I suppose one could code a method that would=3D20=20
> > a)read the PLC outputs back to I/A
> > b) compare these to the values of the inputs that we think =
=3D=20
> I/A
> > should write
> > c) if there is a difference
> > 1) change the input value (to what is in the PLC,=3D20=20
> > to be most
> > bumpless)
> > 2) change the value back to the correct value=20
> > =3D20
> > This seems to be way too much work for a problem this =
simple.=20
> > =3D20
> > Assuming there is not a good way to force a write, what are =
=3D=20
> my
> > options?
> > =3D20
> > RANT MODE ON
> > I HATE serial communications to PLCs! PLEASE get an=3D20=20
> > FBM or CP based=3D20
> > ethernet solution out soon! And yes I know about=3D20=20
> > integrator 50s and
> > 70s,=3D20
> > and yes Alex, I saw some promising things in Orlando,=3D20=20
> > but I NEED an
> > AB=3D20
> > integrator FBM NOW!
> > RANT MODE OFF
> > =3D20
> > Thanks,
> > =3D20
> > David
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > =3D20
> > ______________________________________________________________=20
> > _________
> > This mailing list is neither sponsored nor endorsed=3D20=20
> > by Invensys
> > Process
> > Systems (formerly The Foxboro Company). Use the info=3D20=20
> > you obtain here
> > at
> > your own risks. Read
> > http://www.thecassandraproject.org/disclaimer.html=20
> > =3D20
> > foxboro mailing list:
> > http://www.freelists.org/list/foxboro=20
> > to subscribe:
> > mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin=20
> > to unsubscribe:
> > mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave=20
> > =3D20
> > =3D20
> > =3D20
> > ______________________________________________________________=20
> > _________=3D20
> > This mailing list is neither sponsored nor endorsed by=3D20=20
> > Invensys Process=3D20
> > Systems (formerly The Foxboro Company). Use the info you=3D20=20
> > obtain here at=3D20
> > your own risks. Read=3D20
> > http://www.thecassandraproject.org/disclaimer.html=20
> > =3D20
> > foxboro mailing list: =3D20=20
> http://www.freelists.org/list/foxboro=3D20=20
> to subscribe: =3D
> mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin=3D20=20
> to unsubscribe: =3D
> mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave
> =3D20
> =3D20
> =20
> =3D20
> =3D20
> =
_______________________________________________________________________ =
> This mailing list is neither sponsored nor endorsed by Invensys =
Process=20
> Systems (formerly The Foxboro Company). Use the info you obtain here =
at=20
> your own risks. Read =
http://www.thecassandraproject.org/disclaimer.html=20
> =3D20
> foxboro mailing list: =
http://www.freelists.org/list/foxboro=20
> to subscribe: =3D
> mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Djoin=20
> to unsubscribe: =3D
> mailto:foxboro-request@xxxxxxxxxxxxx?subject=3D3Dleave=20
> =3D20
> =20
> =20
> =
_______________________________________________________________________ =
> This mailing list is neither sponsored nor endorsed by Invensys =
Process=20
> Systems (formerly The Foxboro Company). Use the info you obtain here =
at=20
> your own risks. Read =
http://www.thecassandraproject.org/disclaimer.html
> =20
> foxboro mailing list: =
http://www.freelists.org/list/foxboro=20
> to subscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin=20
> to unsubscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
> =20
> =20
>=20
> =20
> =20
> =
_______________________________________________________________________
> This mailing list is neither sponsored nor endorsed by Invensys =
Process
> Systems (formerly The Foxboro Company). Use the info you obtain here =
at
> your own risks. Read =
http://www.thecassandraproject.org/disclaimer.html
> =20
> foxboro mailing list: =
http://www.freelists.org/list/foxboro
> to subscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Djoin
> to unsubscribe: =
mailto:foxboro-request@xxxxxxxxxxxxx?subject=3Dleave
> =20
_______________________________________________________________________
This mailing list is neither sponsored nor endorsed by Invensys Process
Systems (formerly The Foxboro Company). Use the info you obtain here at
your own risks. Read http://www.thecassandraproject.org/disclaimer.html
foxboro mailing list: http://www.freelists.org/list/foxboro
to subscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=join
to unsubscribe: mailto:foxboro-request@xxxxxxxxxxxxx?subject=leave
Other related posts:
- » [foxboro] AW: Modbus FBM, was "Back to forcing an ABSCAN to